July 6, 20233 yr Hi I have 3 US2000 Pylontech Batteries and recently have added a UP5000 as a master. Can you please assist me with the Dip code settings as currently I have the UP5000 all set up and the US2000 dip codes all set down? Your assistance will be really appreciated.
July 6, 20233 yr 1 hour ago, Ryan Middleton said: Hi I have 3 US2000 Pylontech Batteries and recently have added a UP5000 as a master. Can you please assist me with the Dip code settings as currently I have the UP5000 all set up and the US2000 dip codes all set down? Your assistance will be really appreciated. Hi, hope this will help If you are using RS485 for BMS comms, switch dip switch 1 to ONand leave the rest on off on your UP5000. On the rest of the batteries, leave the switches on OFF. If you are using CAN, Leave all the dip switches off on all batteries including the UP5000. Take note that on the UP5000 your dip switches are upside down as show on the screen short above. But 1 is still one and 2 is still two. ON is ON and OFF is still OFF, this can be confusing to others but 😁 Edited July 6, 20233 yr by hoohloc