Require help with Growcol 3kVA

Featured Replies

Hello Everyone

 

I have recently purchased the following inverter.:

https://onlineshop.gcsolar.co.za/product/growcol-vm-3k-value/

It came with a Pylontech UP2500

https://onlineshop.gcsolar.co.za/product/pylontech-up2500-2-84kwh-li-ion-solar-battery-24v-can-connection/

And the cable set

https://onlineshop.gcsolar.co.za/product/cab-pk-pylon-lv-for-c/

 

I'm connecting it to a 545W Longi Panel. However even using the User settings and setting a Bulk charging voltage of 27.6V and a Floating charge voltage of 27.0V. I'm still getting issues charging the battery. I have tried creating a BMS cable for the inverter as the one provided in the cable pack does not work.

 

I have been able to communicate with the inverter using MultiSIB Control. And the inverter detects the battery as 87%-88% full, most likely due to the voltage of the battery, however on the Pylontech it is only about 50% full.

I have also tried the below links to make a suitable BMS cable but nothing works. Can some assist in this regards. The inverter is the same/similar to an Axpert Mks3-24V. Thank you.

 

 

Looking at the data sheet charge volts is 28.2 to 28.8v but recommended float and bulk volts 28.4v so your float charge in use mode is to low .

 

  • Author
9 hours ago, GMAC said:

Looking at the data sheet charge volts is 28.2 to 28.8v but recommended float and bulk volts 28.4v so your float charge in use mode is to low .

 

I shall change it, although this is one of those inverters with the floating charge bug it would seem as well. It's just the same as the Axpert and Kodak and so on. Just a different casing. I still want the BMS to communicate with the inverter as the battery SOC indicated on the inverter doesn't match against what is shown on the battery itself.

  • 2 weeks later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.