Growatt SPF 5000 ES Parallel connection

Featured Replies

Hello

 

I've got 2 Growatt SPF 5000 ES, i want to connect them to a parallel mode, single phase output.

 

The question is, can i feed in each of the units with different phase from the grid, or they should be feed in with the same phase of the grid?

One phase will not be enough to me.

 

if not possible to use 2 different phases, is it possible to configure the 2 units to work with 2 phase system also for the output (instead of 3)?

 

Thanks

Arthur

  • Author
 

You won't be able to sync them from 2 phases,you can run them as 2 seperate inverters on 2 phases but this isn't making sense,how won't a single phase be enough? Or is the issue you need to back up 2 phases?

the feed in phases are 23A 230V each. the loads is about 10KW, so in order to provide it i need to use 2 23A phases of 3.

if i will run them as 2 separate inverters, should i connect any communications cable between them as they are going to be connected to the same battery?
 

  • Author
 

Running Split Phase mode (not connecting the Current Sharing cable)

thanks for your answer.

just to be sure, i feed in each inverter with different phase (240V each phase) of the grid and on the output of both inverters i will get a single phase of 240V that i can combine in to a one switch?

PS

my Growatt 5000 es is Europe version, not US

 

thanks for your answer.

just to be sure, i feed in each inverter with different phase (240V each phase) of the grid and on the output of both inverters i will get a single phase of 240V that i can combine in to a one switch?

PS

my Growatt 5000 es is Europe version, not US

No,you can't switch and combine phases like that

 

Why do you have such low amperage phases? This makes zero sense

  • Author
 

No,you can't switch and combine phases like that

 

Why do you have such low amperage phases? This makes zero sense

because the solar system is connected to a sub panel that connected with thin cables that i can't replace.

so i guess that i need to configure the two units as a 3 phase system but without the third phase inverter

  • Author
 

Are you confusing multiple inputs and multiple phases possibly? Or is the Main DB 3 phase and has 3 phases into your Sub DB?

Main DB 3 phase and has 3 phases into Sub DB

The main has 40A each phase and Sun has 25A each phase

  • Author
 

Ah alright,you'll need to install a 3-phase to single-phase transformer before the load then to combine phases

Thanks, i probably will buy another Inverter and make it 3 phase system for the house

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.