Huawei PV Inverter max output power?


PJJ

Recommended Posts

Hello guys

We are considering getting one of the Huawei SUN2000 36KTL inverters for the farm, and we can always add more later if we want more PV, but my question here is, what is the max output power (Grid + AC from PV) that the inverter can pass?

Because we only want to install 30KW worth of panels for now, but our total power draw on a nice warm day goes over 150Kva, the only indication I get is a "Max Output current" rating that is stated as 60.8A, meaning (60.8 x 3) * 380V =  70Kva?

 

Thanks in advance!

Edited by PJJ
Link to comment
Share on other sites

Huaweis  don't pass current they augment current to the max of their ability. So if the inverter is producing 25kW and the load is 75kW then 50kW comes from Eskom. The 50kW does not pass through the inverter. The inverter's output is added to eskom rather than the otherway around.

 

Link to comment
Share on other sites

12 minutes ago, Chris Hobson said:

Huaweis  don't pass current they augment current to the max of their ability. So if the inverter is producing 25kW and the load is 75kW then 50kW comes from Eskom. The 50kW does not pass through the inverter. The inverter's output is added to eskom rather than the otherway around.

 

Thanks Chris!

But how does the Huawei know how much current is required?

Link to comment
Share on other sites

2 hours ago, PJJ said:

Hello guys

We are considering getting one of the Huawei SUN2000 36KTL inverters for the farm, and we can always add more later if we want more PV, but my question here is, what is the max output power (Grid + AC from PV) that the inverter can pass?

Because we only want to install 30KW worth of panels for now, but our total power draw on a nice warm day goes over 150Kva, the only indication I get is a "Max Output current" rating that is stated as 60.8A, meaning (60.8 x 3) * 380V =  70Kva?

 

Thanks in advance!

No, In a triphase System, Aparent Power=1.71*380*60.8= 39.507 VA

Edited by Javi Martínez
Link to comment
Share on other sites

1 hour ago, Chris Hobson said:

Hi You install a Huawei Smartlogger and enable its grid limiter function. It then gets the mix of solar and Eskom right so that you do not feed into the grid.  Yesterday visited a Huawei install I did in April and tweaked some of the settings. 

Thanks for the info Chris!

I also assume I could then later add more Huawei units in parallel and all of them connect to one smartlogger?

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...