Hi Guys. 
Bit new to Sunsynk. 
Have a 50kw 3p unit 
2 x 60kw HV batts. 
Grid 80A 3P
Want to implement peak shaving to limit the grid usage to 40kw. 
We enabled the peak shaving at 40kw but the system just used battery power for the total load and did not use the grid at all. 
It stopped when it reached the min SOC. 
What am i missing?

Link to comment
Share on other sites

3 hours ago, Voltageza said:

Hi Guys. 
Bit new to Sunsynk. 
Have a 50kw 3p unit 
2 x 60kw HV batts. 
Grid 80A 3P
Want to implement peak shaving to limit the grid usage to 40kw. 
We enabled the peak shaving at 40kw but the system just used battery power for the total load and did not use the grid at all. 
It stopped when it reached the min SOC. 
What am i missing?

Did you activate your timer and used SOC levels and also start the timer settings at 00h00.

Try by using say a highish SOC while testing 

Here is an example. 

 