February 23Feb 23 I have a Infini 10KW 3-Phase and recently Utility/Electricity company placed a peak export limit on consumers. My export can't exceed 5KW at any time during the day. Is it possible to limit export to grid or restrict PV generation to 5KW, without using CT or smart-meter? Edited February 23Feb 23 by LionKing
February 24Feb 24 Author I got the SolarPower software and connected via USB to the inverter. As per manual on Parameter Setting 2 page, there should be an option for "Max. Feed-in grid power" but it's missing? I'm only seeing following options:
February 25Feb 25 Author I got version 1.14SP8 of SolarPower and set Max. Feed-in grid power setting to 5,000. It reduced grid export without requiring a smart meter or CT, so I'm compliant with the grid now.Details: https://powerforum.co.za/topic/326-infinisolar-3k-plus-factory-password/page/3/#findComment-227000
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.