What tests should I have run on the existing house system before I install an inverter?

I would like to make sure everything is OK.

 

Edited by Mistral

9 minutes ago, Mistral said:

What tests should I have run on the existing house system before I install an inverter?

Test the earth leakage. And test your bonding.

An earth leakage tester costs around R300. Beg, borrow or steal. Or pay a sparky an hour of his time.

Use a digital multimeter (DMM) on the AC voltage range and measure from neutral to earth on any outlet or even inside the distribution board. You want to see less than 1 volt, preferably as close as possible to zero.

An earth loop test might also be a good thing, but only a sparky can do that kind of thing. That's where they use a special meter to test the actual impedance of your earth connection to a spike in the earth. Must be below 30 ohms or 25 ohms, I forgot. The lower the better.

So summary:

1. Earth to Neutral voltage must be as close to zero as possible (they are bonded so ideally it should be zero, give or take a few millivolt).

2. Earth leakages tested for proper operation

3. A good earth for the whole installation.

That's a good starting point.

Would also recommend to make sure that the breaker and wires are sized correctly. And circuits are identified properly. i.e. if you switch a light circuit off that only lights and not plugs go off, I had both these problems when COC was done on my new place.

If COC done recently, then you should be good to go. 

On 2019/04/17 at 12:50 PM, plonkster said:

Test the earth leakage. And test your bonding.

An earth leakage tester costs around R300. Beg, borrow or steal. Or pay a sparky an hour of his time.

Use a digital multimeter (DMM) on the AC voltage range and measure from neutral to earth on any outlet or even inside the distribution board. You want to see less than 1 volt, preferably as close as possible to zero.

An earth loop test might also be a good thing, but only a sparky can do that kind of thing. That's where they use a special meter to test the actual impedance of your earth connection to a spike in the earth. Must be below 30 ohms or 25 ohms, I forgot. The lower the better.

So summary:

1. Earth to Neutral voltage must be as close to zero as possible (they are bonded so ideally it should be zero, give or take a few millivolt).

2. Earth leakages tested for proper operation

3. A good earth for the whole installation.

That's a good starting point.

Good advice!

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.