April 17, 20197 yr What tests should I have run on the existing house system before I install an inverter? I would like to make sure everything is OK. Edited April 17, 20197 yr by Mistral
April 17, 20197 yr 9 minutes ago, Mistral said: What tests should I have run on the existing house system before I install an inverter? Test the earth leakage. And test your bonding. An earth leakage tester costs around R300. Beg, borrow or steal. Or pay a sparky an hour of his time. Use a digital multimeter (DMM) on the AC voltage range and measure from neutral to earth on any outlet or even inside the distribution board. You want to see less than 1 volt, preferably as close as possible to zero. An earth loop test might also be a good thing, but only a sparky can do that kind of thing. That's where they use a special meter to test the actual impedance of your earth connection to a spike in the earth. Must be below 30 ohms or 25 ohms, I forgot. The lower the better. So summary: 1. Earth to Neutral voltage must be as close to zero as possible (they are bonded so ideally it should be zero, give or take a few millivolt). 2. Earth leakages tested for proper operation 3. A good earth for the whole installation. That's a good starting point.
April 18, 20197 yr Would also recommend to make sure that the breaker and wires are sized correctly. And circuits are identified properly. i.e. if you switch a light circuit off that only lights and not plugs go off, I had both these problems when COC was done on my new place. If COC done recently, then you should be good to go.
April 21, 20197 yr On 2019/04/17 at 12:50 PM, plonkster said: Test the earth leakage. And test your bonding. An earth leakage tester costs around R300. Beg, borrow or steal. Or pay a sparky an hour of his time. Use a digital multimeter (DMM) on the AC voltage range and measure from neutral to earth on any outlet or even inside the distribution board. You want to see less than 1 volt, preferably as close as possible to zero. An earth loop test might also be a good thing, but only a sparky can do that kind of thing. That's where they use a special meter to test the actual impedance of your earth connection to a spike in the earth. Must be below 30 ohms or 25 ohms, I forgot. The lower the better. So summary: 1. Earth to Neutral voltage must be as close to zero as possible (they are bonded so ideally it should be zero, give or take a few millivolt). 2. Earth leakages tested for proper operation 3. A good earth for the whole installation. That's a good starting point. Good advice!
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.