September 2Sep 2 I have all my loads connected to my Deye inverter. I don't have any non essentials. I'm using Zero export to Load. Is the CT required? Installer put the CT next to inverter which is 25m away from the main db
September 2Sep 2 I recall in one of Keith Gough's Sunsynk training videos that the CT coil is required regardless. The 25m distance should not be a problem as long as you keep the twists in the connecting wires, which reduce EMI.