Everything posted by Yellow Measure
-
Sunsynk 8kw charge rate
From the LiBMS screen, I can see that you have good battery comms, also that the BMS is limiting charge and discharge to 160A, for whatever reason (it may be an earlier revision of the R100 that had this limitation). Interestingly enough, I cannot get a specsheet or manual from official Revov sources, but I Iocated a Revov R100 manual that states that 30A is the recommended charge rate. https://www.manualslib.com/manual/2888737/Revov-R100.html?page=1#manual Was the LiBMS shot taken during the day, full sunlight, or at night? Can you take a shot during the day when it starts charging from PV? Also, do you have an official manual / specsheet for your Revov batteries that you can share? On the first battery screen, I see that you have set the battery to 200Ah, that is correct for the two R100s in parallel. Why did you choose 130A for charge and discharge, and not the combined maximum continuous charge amps and maximum continuous discharge amps of the two batteries in parallel? Does your revision of the R100s only allow 65A charge and discharge rates? It effectively limits your 8kw inverter to deliver only a little over 6kw when drawing from the battery at night. Is that how you want it? On the 2nd battery screen, I see that you are limiting Generator (Aux port) to charge at a maximum of 40A, and Grid charge to a maximum of 130A, yet neither are ticked to allow charge. I guess that to do not wish to charge batteries from grid or genny at all? Do you have a genny connected to the Aux? What firmware revision level are you running? Is it current? Can you provide a pic of the settings screen where this is displayed? Can you also provide a screenshot of the Battery Shutdown screen? And lastly, may be a silly question, but I have to ask it: how are your PV strings configured? 2 strings with the panels in series?
-
Sunsynk 8kw charge rate
Hello and welcome to Powerforum. Your 8K SS is capable of charging at 190A, and the R100s should be capable of accepting 100A each, so 200A when in parallel. The SS is compatible with the Revov's BMS using CANBus protocol 0. You should be charging at well over 7Kw with that array on a sunny day (depending of course on your loads, orientation and azimuth of panels etc.). Check your CANBus comms cable (Inverter to master battery) and master to slave battery link. If you don't spot any issues, please share your LiBMS screen, as well as battery setup screens?
-
Pylontech batteries issues
Where did you get the Dyness Powerbrick rated at 300A? Dyness Global site has the Powerbrick and Powerbrick Plus (which is not available in SA), both at 14.336kWh and 140A / 0.5C (Continuous). Yes, it can peak at 300A, but not continuous. Why? My 32kWh bank feeds a 5k inverter.
-
Pylontech batteries issues
OP has an 8kW Multiplus last time I checked, 2x Knyee in parallel is ample: will deliver 9.6kW @100A with peaks of 19.2kW at 200A. It's an interesting limitation, and I suspect that Knyee are being ultra conservative. I have 2x 16.08kWh HinaESS PowerGem Max, which is the white-labelled version of the Knyee, was also supplied by @Powerforum Store and its datasheet states 200A continuous max. discharge per unit.
-
Pylontech batteries issues
2x 16K Knyee will cost R60,720.00 Sell the balance out of hand. Power Forum Renewable Energy Store | By Powerforum.co.zaKNY-ES-LV-16 16.08 kWh 314 AMP Floor-Type LiFePO4 Battery51.2V 314Ah (16.08kWh) floor-standing LiFePO4 energy storage battery – Model KNY-ES-LV-16 from KNYSE Energy (part of the reputable Chilwee Group).This is a solid, no nonsense battery that delivers gre
-
Price Drop SPECIAL DEAL ALERT – Hinen Compact Back-up System (TDB) with 2 x 580 Watt Astro Energy Solar panels R18 587,91 VAT Incl. – Limited Stock!
It should not be too much of a hassle if not, can easily be made up. Nothing special about MC4 solar panel connectors or the coaxial power connector (also known as a DC barrel connector).
-
Off Grid Reno - 12/16kw Deye or Sunsynk?
Agreed. And if the feedback rates improve, those with large battery banks and oversized arrays could consider selling or wheeling themselves.
-
Off Grid Reno - 12/16kw Deye or Sunsynk?
Flexibility, if / when adding another possibly larger inverter which could fulfil the role of grid.
-
Off Grid Reno - 12/16kw Deye or Sunsynk?
6-7 years ago Sunsynk was top of the pops, the darling of installers and homeowners alike. That honeymoon period has expired and lots of water has passed under the bridge. Their South African country manager (David Drake at the time) made written promises of loaner units for repairs / swop-out under warranty, which were later dishonored and rescinded, and which left a bad taste in many people's mouths. The Sunsynk is not a bad inverter at all, I have one that hasn't skipped a beat for the past 6+ years. I have another that had a calibration issue since day one, which ought to have been returned under warranty, but I haven't done it (since 4 years ago) because it would inconvenience the client to be without a unit for the 6-8 weeks that it takes to decommission, ship, await repairs, reship and re-install. It's OK, does what it says on the box, but today it is hardly worth the price premium. If I were to turn the clock back, in hindsight the Deye would have been the better choice (at the time). If I were to do the same installations again today, I would rather install a Solis S6 series, far better support and warranty, and far more advanced technically than any Deye / Sunsynk, as well as a far cheaper price. Moreover they are a Tier-1 manufacturer with an excellent global reputation vs the Sunsynk / Deye's tier-2/3 status (at best). Let me put it this way: If my own personal Sunsynk blows up today, I wouldn't even shop around, I would gladly replace it with a Solis S6 in a heartbeat. The 16K Solis S6 made its debut in April this year, the 5, 6, 8 and 12K quite a few months earlier than that. Check out Powerforumstore's reviews on the S6 range, they are great.
-
6200VA / 6200W Ecco Solar Ready Hybrid Inverter Trolley 5.12 KWh Lithium Battery
You make a good point, I was seeing it as an off-grid portable point solution, and it can only function as an off-grid inverter if it is Franken-monstered into a "solar house". Not impossible, but potentially troublesome. It's still overpriced though, compared to the far more extensible and feature-rich the Hinen / Knyee combo at R18,342.50: 11.4kW solar input vs 6.5kW ; 2x low amperage MPPT vs 1x high amperage MPPT; Parallel capable; Hybrid connection possible vs off-grid; Integrated Type II DC SPD & Type III AC SPD (amazing!); Built-in aerosol fire extinguisher; 10-Year Warranty vs 5 on inverter only. Power Forum Renewable Energy Store | By Powerforum.co.zaHinen H6000-EU 6kW Hybrid Inverter + Knyee ES-LV-5 5.12kW...Combo DEAL: Hinen H6000-EU 6kW Hybrid Inverter + Knyee ES-LV-5 5.12kWh Wall-Mounted Battery Combo High Performance Ultra-Quiet Advanced Safety 10Year Warranty
-
Looking for Hubble Batteries, 5kw am2
-
6200VA / 6200W Ecco Solar Ready Hybrid Inverter Trolley 5.12 KWh Lithium Battery
This is cheaper, same size battery, half the wattage but more than enough for TV and laptop.
-
Looking for Hubble Batteries, 5kw am2
Powerforumstore. https://powerforum-store.co.za/collections/batteries
-
Impact high consumption devices have on batteries
You reminded me of something quite important, which I forgot: Whilst house-hunting during 2019, I made a point of only viewing properties with: a clear W-->N<--E view; and 0 degree azimuth (10-15 degrees max either side); and a roof that can take 24+ panels. I did not have to look long for a suitable home, and having made my wishlist upfront helped a lot.
-
Impact high consumption devices have on batteries
I have a Sunsynk 5K, 6kWp on roof since 2020, and recently upgraded storage to 32K Hina (Knyee white-label), been off-grid since January 2026. I have been optimising usage and current drain over the past 6 years: Outdoor heatpump for hot water; Gas stove, oven is still AC, but I built a Pizza oven outside (and a whole outdoor kitchen too!); Added 2x Inverter aircons (24000 + 18000 BTU); Gas heater; Slowly migrated current hungry devices, like firewall / router / NAS / security cameras / NVR to fanless low current models; Don't operate Class-A amplifiers continuously, or moved to Class-D. Next on the list is the fridge freezer, eyeing a Bosch AAA+ model. Optimising a power budget is basically the same as running a bank account: You either create more income, or you cut / replace expenses, or a combination.
-
Exciting Official Powerforum Review – Knyee Energy ES-LV-16 16.08kWh Floor Type Battery in a Real Off-Grid Micro Grid!
Indeed, even the Tesla Powerwall 3 has a charge rating of 0.37C and a discharge rating of 0.85C.
-
Kwikot Elon Smart - please check my work
And that's how savings are achieved, whilst balancing lifestyle options. It uses the solar panels' DC in a super-efficient way to heat the water, but ensures that, regardless of solar conditions, you and you family will always have a warm shower (even if you have to pay extra for it). It's still just a better mousetrap though, and will suffice if you have zero aspirations of becoming completely independent from the municipality for electricity.
-
Kwikot Elon Smart - please check my work
...if the temperature of the water in the geyser is insufficient. Otherwise it will do nothing. ...if the temperature of the water in the geyser is insufficient after a whole day of using the DC power from solar. Any "smart" system is fallible, you always need an override.
-
Kwikot Elon Smart - please check my work
How does that help the Elon decide on whether to use DC or AC to power the geyser?
-
Kwikot Elon Smart - please check my work
FYI: I am not the OP. And according to the product write-up (which is publicly available BTW) it's a little more complex than that, apparently it analyses usage patterns, time of day and other factors.
-
Kwikot Elon Smart - please check my work
It doesn't, it uses a "smart" thermostat to choose whether or not to drive the existing element via DC, or to use AC from the grid.
-
YkonWorx S3Es1
Hello @holtand is there something that we can assist you with?
-
empowering myself
Yellow Measure replied to Inevitability's topic in Starting In Solar? Feel free to introduce yourselfAfter reading your posts, and understanding your approach (and limited budget), I think that it's worthwhile to think about the ultimate end-state as well as "systems thinking" in your visioning. First-off: Good on you for focusing on the biggest culprit, and the area where the most possible gains can be realised. Secondly, be mindful that you don't lose your peripheral vision in the process. People with limited budgets can rarely, if ever, create their dream system in one big bang. Each component is one building block of the bigger system, like a grain of sand in the mortar, the mortar holding one brick to another, a brick in a wall of bricks, a wall in a room, a room in a house, and a house in a home. Each component should be reusable. Even wealthier people make this mistake, and those that aren't as wealthy are prone to do so because of "sticker shock", or they limit their big-picture thinking because they are either 1) unable to prioritise their spending, or are 2) unable to see how the gradual spending / investment of smaller amounts eventually adds up to total independence from the Socialist Eskom / municipality. 6 years ago this wasn't my own goal, but in January the greedy socialist municipality forced me to choose it, at very little cost to myself because the foundation was solid. Today you are solving one problem, but tomorrow will bring another, and so your solution needs to be extensible and not just a "point" or standalone solution. A parallel can be drawn to those that purchase Mecer trolleys to "keep the TV on" during loadshedding. It was a great solution at the time, for short periods of outage, but the downsides were that it was clunky, required a place to stay and trip-me-over extension leads, emitted explosive hydrogen gases, produced motor-killing square waves and was subject to the shallow cycles and maintenance requirements of lead-acid batteries. Woe betide anyone who had a surge-protector after the inverter, or who had plugged them into wall sockets when the power returned. When load-shedding intensified, some people simply bought more of them, so we found households with two or three of them. Those who were smart enough to realise that Eskom's inability to keep the lights on, as well as their constant billion rand bail-outs and price increases was endemic to Socialist agenda, went for solutions earlier on that were more extensible and could be upgraded without risk of the big BOOM! Granted that point solutions have their place: a 10,000mAh power bank is useful and portable, and can be repurposed in hundreds of different ways, but it isn't a power or money saver. Many who have had solar-powered geysers before installing a full-blown integrated solar system argue that in hindsight, precious North-facing roof space used by the solar geyser heating system would be better served if they could replace it with traditional solar panels, purely because the electricity generated could be redeployed to either charge batteries or service other loads Someone who seems to have achieved his clear objectives (off-grid!) in record time, and very limited budget is @Denns in his post https://powerforum.co.za/topic/34183-exciting-long-term-review-new-hubble-energy-am16-am5-in-a-real-micro-grid-setup/#findComment-230500 You can bet that he didn't arrive at it all in one month though, so I leave it to him to expand on his journey and budget, which I am sure that you will find to be inspirational.
-
Exciting Long-Term Review: NEW Hubble Energy AM16+ & AM5+ in a Real Micro-Grid Setup
Indeed, especially when they are a mix of LiFEPO4 and NMC. Impressive.
-
Huge Sonoff Giveaway!
And I discovered some more treasure! https://sonoffafrica.co.za/treasure/