May 9, 20197 yr How many amps per pylontech us3000b battery must be used in the setup for Victron Quattro ESS setup. I know for the us2000b plus you use 50 amps. Thanks.....
May 10, 20197 yr 12 hours ago, Harryc said: How many amps per pylontech us3000b battery must be used in the setup for Victron Quattro ESS setup. If you turn on DVCC the battery will communicate with the Venus device and do this for you. But generally it is 35A per module.
May 10, 20197 yr 11 hours ago, plonkster said: If you turn on DVCC the battery will communicate with the Venus device and do this for you. But generally it is 35A per module. I thought @Harryc was referring to the Ah capacity of the battery, the US2000 is 50Ah and the US3000 is 74Ah. This is from the "Victron & Pylontech US2000B and Phantom-S" document. https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom
May 11, 20197 yr 13 hours ago, VisN said: was referring to the Ah capacity of the battery, the US2000 is 50Ah and the US3000 is 74Ah. Right. It is a bit unclear init? The capacity is 50Ah for the smaller module and 74Ah for the larger one. But the charge and discharge rates are C/2, hence 25A and 35A per module.