July 22, 20197 yr Hi guys i just want to clarify something.Am i correct that only the 3000 kva models of Victron are on the list. Am i allowed to string 2 together ?
July 22, 20197 yr 37 minutes ago, vulgrim said: Hi guys i just want to clarify something.Am i correct that only the 3000 kva models of Victron are on the list. Am i allowed to string 2 together ? Correct but the 5kva is in the process of coming onto the list I'm told. Yes you can string two together but the problem is you will be exceeding the i.e. 3.5kw limit on a 63amp breaker as per SANS and NRS regulations. Edited July 22, 20197 yr by Guest