September 2, 20206 yr Good day. I have a 8kw sunsynk inverter, 16x320 pannels and 2x3.5 kw batteries. The db has been split into separate neutrals. The issue i have is that the main db earth leakage trips as soon as the main power is cut(load shedding). Any idees?
September 2, 20206 yr 1 hour ago, Charlesk said: Good day. I have a 8kw sunsynk inverter, 16x320 pannels and 2x3.5 kw batteries. The db has been split into separate neutrals. The issue i have is that the main db earth leakage trips as soon as the main power is cut(load shedding). Any idees? Did you bond the neutral in the inverter. There's a video on the sunsynk website explain the earth bond using a relay. I also have the 8kw sunsynk inverter but all my loads are on the invert so didn't do the earth bonding and don't have any trips.