1 hour ago, Charlesk said:

Good day. 

I have a 8kw sunsynk inverter, 16x320 pannels and 2x3.5 kw batteries. 

The db has been split into separate neutrals. The issue i have is that the main db earth leakage trips as soon as the main power is cut(load shedding). Any idees? 

Did you bond the neutral in the inverter. 

There's a video on the sunsynk website explain the earth bond using a relay. 

I also have the 8kw sunsynk inverter but all my loads are on the invert so didn't do the earth bonding and don't have any trips. 