I have a MUST 5KVA inverter (Unfortunately no BMS functionality), 2x Pylontech US3000 batteries and 12x Canadian Solar 330W panels.

1. I wanted to find out what one would recommend, for the inverter settings (i.e. charging currents grid/utility, bulk charging voltage, float voltage, low dc cutoff, stop charging voltage when grid available)

2. What settings would I then to need to use to marry my Victon battery monitor (BMV-700)

Thanks

Posted
6 hours ago, Sheyn said:

1. I wanted to find out what one would recommend, for the inverter settings (i.e. charging currents grid/utility, bulk charging voltage, float voltage, low dc cutoff, stop charging voltage when grid available)

Charging 74A (2x37A) or closest value below this

Bulk: 52.5V

Float: 51.8V

Back to grid voltage: 48V (this is where you need to play around and figure out what works best for you - and ensure that you stay above 20% SOC. The BMV will help you getting the right voltage)

Low cutoff voltage (when your system shuts down): 46V

Posted
13 hours ago, wolfandy said:

Charging 74A (2x37A) or closest value below this

Bulk: 52.5V

Float: 51.8V

Back to grid voltage: 48V (this is where you need to play around and figure out what works best for you - and ensure that you stay above 20% SOC. The BMV will help you getting the right voltage)

Low cutoff voltage (when your system shuts down): 46V

Thanks fort the helpful suggestions

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...