wtjaden Posted November 13, 2020 Share Posted November 13, 2020 (edited) Hope someone can help with the Pylon BMS connection problem installed a axpert Max 7.2 kw and a 3rd gen Pylon us3000c. Made a custom cable using the pin outs for the king. however when connecting the battery the Pylon beeps 3 times after a wile and i see a error 61 on the display. watchpower also reports a eeprom error. Do anyone know if there's a different pin out for the axpert max ? and could the axpert firmware be incompatible with the latest 3rd gen Pylon US3000c? Edited November 13, 2020 by wtjaden Quote Link to comment Share on other sites More sharing options...
wtjaden Posted November 16, 2020 Author Share Posted November 16, 2020 Solved this issue right is the Battery left inverter so battery pin 8 to inverter pin 3 and battery pin 7 to inverter pin 5 Proxicon and Gerrie 2 Quote Link to comment Share on other sites More sharing options...
Ian W Posted November 22, 2020 Share Posted November 22, 2020 On 2020/11/16 at 9:57 AM, wtjaden said: Solved this issue right is the Battery left inverter so battery pin 8 to inverter pin 3 and battery pin 7 to inverter pin 5 Many thanks, the Cable I received in my 5KV Kodak King 3 weeks ago is the same as this, what made it all work was using this cable and on the Pylontech Battery Dip1 up (1) and inserting the RJ45 into RS485 socket on the battery... Now the battery icon flashes and its all happy using PyL on inverter setting 05. Still currently discharging to check battery shutdown.. Ian Quote Link to comment Share on other sites More sharing options...