I see that you have a 50A breaker to send power to the inverter, this would required at min a 10mm cable to the inverter, the inverter neutral shows it is fed from the neutral bar, i assume this just to be an error with the diagram. The earth leakage you have after the inverter should probably have a tripping current of 63A, some off these are only earth leakage and not over current devices , as this is way too high for the inverter i would rather have a 30A breaker feeding the earth leakage, assuming you are using at min a 4mm cable from the inverter.