1. what is the VOC of the panels?

2. the 5kw can handle 6500w max , you have more than 8kw of panels if you use a 205 loss you are just within the limits. If you have a cold day you might exceed the max

if the panels VOC is 45v then use 2 strings of 10  per MPPT that gives you 6700w and should be save.

 

 

Link to comment
Share on other sites

3 strings of 8 panels, as long as VOC total does not exceed the stated max, for safety I would go at least 10% less than max. The sunsync can handle the extra pv amperage per mppt input, it simply will not use the extra amperage that is available on the particular mppt input (according to the SS guys themselves)

Possibly, 8S panels E + 8S panels W (in parallel on mppt1), the last 8S panels on a north pointer.... Depending on your geography and mounting availability...

That might be the best to stretch the daylight...

E