Shoto SDC10-Box 5 (5.12kWH) 16 Cell, battery settings
Thank-you @jumper.
-
Shoto SDC10-Box 5 (5.12kWH) 16 Cell, battery settings
@jumper, Is the timed absorb setting set via Program 32 (equalisation charging time) on my Axpert inverter?
-
Shoto SDC10-Box 5 (5.12kWH) 16 Cell, battery settings
Thank-you @jumper. I will action as per your proposals.
-
Shoto SDC10-Box 5 (5.12kWH) 16 Cell, battery settings
My Axpert Mecer 5KW inverter is connected to a Shoto 5.12kwh (16s) lithium battery. This is setup purely as a backup system - no solar. The inverter and battery BMS are monitored via Solar Assistant. I have the following battery settings enabled on the inverter: I'm encountering a phenomenon where the grid charges the battery to only 96% state of charge (SOC). Following this, the battery gradually discharges to reach the float charge voltage. Several hours later, the SOC percentage begins to decrease gradually and continues to fall over the course of several days. I would greatly appreciate any insights into the possible reasons for this and any advice on how to address the problem.
-
Mecer SOL-I-AX-5P64 Axpert Inverter and SHOTO SDC 10-Box5 5.12kw battery settings
Hi, I have the same setup. Did these battery settings above resolve your SOC % discrepancy between SA and the battery? Are you able to reach 100% SOC? I'm encountering a phenomenon where the grid charges the battery to only 96% SOC as indicated on SA. Following this, the battery immediately discharges to reach the float charge voltage of 54v. Several hours later, the SOC percentage begins to decrease gradually and continues to fall over the course of several days.
-
Axpert Mecer Inverter and 5.12kwh Shoto SOC
My Axpert Mecer 5KW inverter is connected to a Shoto 5.12kwh (16s) lithium battery. This is setup purely as a backup system - no solar. The inverter and battery BMS are monitored via Solar Assistant. I have the following battery settings enabled on the inverter: I'm encountering a phenomenon where the grid charges the battery to only 96% state of charge (SOC). Following this, the battery gradually discharges to reach the float charge voltage. Several hours later, the SOC percentage begins to decrease gradually and continues to fall over the course of several days. I would greatly appreciate any insights into the possible reasons for this and any advice on how to address the problem.
-
Sunsynk 5kw Inverter model numbers
I’m considering going the Sunsynk 5kw 1P 48v route, but researching the inverter I find different models in that range e.g. SG01LP1 with 02, 03, P2, EU etc variations. What are the differences? Which is the latest Sunsynk 5kw 1P 48v model in ZA?
-
Importance of Inverter talking to BMS
Thank-you very much.
-
Importance of Inverter talking to BMS
Thank-you for sharing these settings. I have a Mecer 5KW and my Shoto 5.12 16S arrived this week. Would you mind sharing your current inverter voltage settings used to manage your Shoto?