Good day to all
I am preparing and mounting components required for an Inverter and Battery installation before our electrician will come to finalize the installation. I have a few questions regarding the MCB for the Inverter (Inverter Output) on the Essentials side.
The Sunsynk Datasheet for a 5.5KW model states a Max Continuous AC Pass-Through current of 35A.
May I assume that this will still be the Max Pass-Through current when the Grid is active?
If so... the manual states a 32A breaker on the essentials side but would a 35A be good or would I rather stick to the 32A breaker?
My house is wired in a rather limited way with only 2 lights breakers and 2 plugs breaker which limits my choice of plugs to put on the Essentials side without re-wiring. I will of course have a ChangeOver switch between Grid, Inverter and Essentials Side. If I move both plugs breakers to the Essentials side but still wanted to not limit myself when having the Grid power the Essentials Side (Grid selected on ChangeOver) then could I put the Inverter Output Breaker (35A) before the ChangeOver but have a 63A breaker after the ChangeOver? Wiring will obviously match the breakers required. See attached image.
Thank you