pintopf got a reaction from Jesus Abril in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI think, a noise-free version doesnt exist,because a minimal air convection must exist.
In my VMIII Twin - 400W works with DSP Firmware Version 60.95 and Display 25.12.
In this 60.95 version are the fans are controlled by temperature and under less output power the fans produce less noise.
I think, this version is a good compromise between cooling and noise.
-
pintopf got a reaction from Coulomb in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINThank you for the new version 68.13 !
Yesterday i put this version in my VM III twin 4k and its work fine, but i think, that the internal measurements of the inverter are in this version very optimistic. I have an offset on the battery charging output of +4A, that means, if no current flows, the axpert shows me 4A. Also the internal measurement of the solarpanel-current are above 150-200V Voltage more than twice as high as in reality. Under this voltage, the display shows the correct value. Badly, it looks like that the internal MPPT uses this wrong values, and the output power is less than it can be. Also, the statistics in dessmonitor shows much to high values.
In december we have short, dark days in germany, so that every watt counts ;-)
My next step was to reinstall the version 60.95 , but by this action my computer gives up and die without any sign of life. I think, that any yovervoltage from the RS232-port from the inverter bricks my computer. The lucki thing was, that i can bring him back to life, with the help of chatgpt.
I bougt an galvanic isolated USB->RS232 interface and installed today the older version 60.95.
I testet also the version 60.87, but in this version are the fans very loud.
Greetings, Peter
-
pintopf got a reaction from علاء من سوريا in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI'm attaching two charts to this message.
Both show the start of the solar system in the morning.
Picture 1 ist with the older modified firmware 160.06 from @Coulomb
Picture 2 shows the same situation with the newer firmware 60.95
Before 8:00 the system is in charge mode (charging only), then the 230V output switches on.
In the first case, the MPPT restarts at 8:00, where the output is switched on, and finds a good working point
In the second case, the MPP tracking starts on its own.
-
pintopf got a reaction from esmail-kassir in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINSee the attachement. The graph shows an 1 hour intervall. Firmware: 60.95
-
pintopf got a reaction from esmail-kassir in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINHere is it :
\x51\x50\x49\x47\x53\xB7\xA9\x0D -
pintopf got a reaction from esmail-kassir in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI attached the file. This file is from this thread, date june,13.
My node-red program sends cyclic the "QPIGS" command to the inverter, and the answer contains also the heat sink temperature.
If the fans run faster under load, the temperature drops, and start to rising under heavy load but reaches never 50°C.
I don't log the temperature but i will tomorrow use 2000 W for some time out of my batterys to show you the graph from the node red -UI.
VM TWIN_Ver60.95.7z
-
pintopf got a reaction from esmail-kassir in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINIf your inverter starts at the first attempt in the morning?
Without grid and power-button "off", my inverter often destroy the EEPROM Data at the interupted boot attempts, as i showed yesterday
Not the same, but with the older display-firmware my battery lost sometimes (1 - 2 times per day?) the conection to the inverter, the battery symbol at the display stop blinking, and the warning shows.
After i installed the new firmware, this never happens again. (or it happens, if i'm not in front of the inverter?)
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI testet it at my 4kW VMIII and the result is: 55W with depressed button and 65W with pressed button.
My mode was "SBU"
I switch an measure the grid with an "shelly 1 PM"
Why do you not use a automatic power transfer switch to solve your problem? I think, that this mode (without battery) is not optimal for the inverter.
I use this switch: (see photo)
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINIf your inverter starts at the first attempt in the morning?
Without grid and power-button "off", my inverter often destroy the EEPROM Data at the interupted boot attempts, as i showed yesterday
Not the same, but with the older display-firmware my battery lost sometimes (1 - 2 times per day?) the conection to the inverter, the battery symbol at the display stop blinking, and the warning shows.
After i installed the new firmware, this never happens again. (or it happens, if i'm not in front of the inverter?)
-
pintopf got a reaction from esmail-kassir in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI had similiar problems in communication between my inverter and the pylontech-batteries.
The display firmware update to version 25.12 fixed it.
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI had similiar problems in communication between my inverter and the pylontech-batteries.
The display firmware update to version 25.12 fixed it.
-
pintopf got a reaction from Coulomb in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINHi @ monsam,
i had a similiar problem with my VMIII Twin / 4kW last year, in my case lost the inverter his serial number.
The problem was, that in the morning, with 230V off and Inverter off (round button not pressed), when the sun begin to shine, the solarpanels create not enough energy for complete startup the inverter, so many attempts were made, until he starts.
Every attempt causes an interrupt in the start-up procedure, and sometimes the EEPROM becames corrupt. You will see it in Watchpower, Energy-Mate or Dessmonitor under "Alarm"
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINHi @ monsam,
i had a similiar problem with my VMIII Twin / 4kW last year, in my case lost the inverter his serial number.
The problem was, that in the morning, with 230V off and Inverter off (round button not pressed), when the sun begin to shine, the solarpanels create not enough energy for complete startup the inverter, so many attempts were made, until he starts.
Every attempt causes an interrupt in the start-up procedure, and sometimes the EEPROM becames corrupt. You will see it in Watchpower, Energy-Mate or Dessmonitor under "Alarm"
-
pintopf got a reaction from Tshegofatso in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI'm attaching two charts to this message.
Both show the start of the solar system in the morning.
Picture 1 ist with the older modified firmware 160.06 from @Coulomb
Picture 2 shows the same situation with the newer firmware 60.95
Before 8:00 the system is in charge mode (charging only), then the 230V output switches on.
In the first case, the MPPT restarts at 8:00, where the output is switched on, and finds a good working point
In the second case, the MPP tracking starts on its own.
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINIs here anybody with an "stuck at 60V" problem with 60.95 software?
Since i installed this firmware, mine MPPT works fine.
I attached a plot from today until now, a cloudless day: ( red: solar voltage ; blue solar current)
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI see, that my inverters MPPT starts if PV-input current reaches 0,2A . (FW 60.95)
With panels in parallel, this current is reached earlyer.
At the beginning of this year, i testet a lot of connections between my panels and my inverter.
I found also out, that 2s 3p was a good solution, but it was a lot of cables in my garden and the current was very high, about 25-30A at around 100V.
After this tests i experimented with TIGO "TS4-A-O" Modul-optimizer (Link ), and they worked nearly perfect in my system. This optimizers reduces the output voltages from the modules and keep the current constant in the system, so thad shadowed modules produces less power which added to the string-power, instead of reducing the overall performance through the little current they produce.
So, the max current is 9A, and the maximum voltage 350V.
Then was only the problem with "Stuck at 60V" with the older firmware, but this has @Coulomb solved.
After i installed the 60.95 firmware, the noise of the fans decreased and the MPPT works fine, without any patches.
Thankfully i used pylontech batteries, so that the discussed battery-problems are not mine.
The picture shows a average day.
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI use a solution with an ESP32 microcontroller, which is connected to the serial interface of the display via a MAX232 converter.
The ESP cyclically sends a "QPIGS" request to the inverter and provides the result via the MQTT protocol via W-LAN.
(Example: String QPIGS = "\x51\x50\x49\x47\x53\xB7\xA9\x0D"; //hard coded string with CRC)
The ESP32 also receives commands via MQTT, appends the CRC16 checksum and sends the result back into the network.
The ESP32 is controlled via my home automation, using NodeRed.
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINThis bug means, that the inverter´s MPPT is stuck at his starting voltage at the begin of a new day, where the brightnes is increasing, until the current of the solar input reaches 200(400?) mA at 60V. The calculation of the output power results in a value that is too low to start the tracking.
If you have some Solarpanels in serial, you reach this current relativ late, you can´t use the first Energy of the day. If you have i.e. 350V panel voltage, are this 70 W (at 200mA)
If the MPPT starting voltage higher, the inverter calculates a higher power and the tracking starts earlyer.
In this thread @Coulomb presents his patched firmware, which sets the starting voltage from the MPP-Tracker to other voltages.
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI'm attaching two charts to this message.
Both show the start of the solar system in the morning.
Picture 1 ist with the older modified firmware 160.06 from @Coulomb
Picture 2 shows the same situation with the newer firmware 60.95
Before 8:00 the system is in charge mode (charging only), then the 230V output switches on.
In the first case, the MPPT restarts at 8:00, where the output is switched on, and finds a good working point
In the second case, the MPP tracking starts on its own.
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINIs there a change log for the firmware versions? Are there Improvements?
I control my inverter with an ESP32, which get the data from the VMIII over serial connection and build up a communication via WiFi (MQTT-Protocol) to my home-automatisation with NodeRed.
Since I don't miss any functions, I conquered my curiosity and didn't install any new firmware yet. 😉
-
pintopf got a reaction from Tarek Yag in Collection of DSP Axpert Firmware for VM III TWIN and VM IV TWINI also tested this version (60.95) and it runs nearly perfectly. My DisplayFW is : 25.05
Much quieter fans at low loads and the heatsink temperature has never been above 45°C.
At higher loads (>1500W) the temperature drops again because the fan(s) then run faster.
The inverter hangs in my basement at around 19°C.
Another positive thing about the software version is the fact that the MPP-Tracker no longer gets stuck at low voltage. So far I've had to use a version modified by @Coulomb so that the voltage doesn't get stuck below 100V.
Thank you for this Software-Version.
Edit:typo