Everything posted by luk88
-
One 10.2kW Y&h inverter jamming the CB and 10m Ham RF bands.
Thank you for the reply. Sadly I was mistaken . It is not the inverter. The preamp for the SDR I was doing the testing with was powered by the inverter so the signals dissappeared when I switched it off. Imagine my surprise when I disconnected the inverter ,put it on my bench. I put grid AC on the line the inverter was powering and the noise came back... So the thread is a bit pointless now.
-
One 10.2kW Y&h inverter jamming the CB and 10m Ham RF bands.
I'm hoping someone can help me with so.e tips what to check as I can't really afford to buy a new inverter because of this. I have two of these inverters and only one is jamming both the CB and the 10m Ham radio bands in the entire neighbourhood when the AC is on. When it is charging the batteries from solar it is fine. When it it powering loads it is even worse. So I know the problem is with the AC inverter module. I'm pretty goid with digital electronics and general repair, but I never dealt with such a problem . To summarise, with the inverter off my RF noise floor as seem on an SDR is about -80dB. The moment I seitch the AC on it suddenly transmits huge signals up to 40dB over the noise floor (up to -40dB jamming even the strongest signals). Mostly at 10Mhz, 5Mhz, 20Mhz and then the worst. A continuous chunk between 24Mhz up to 44Mhz of spikes every few tens of KHz raising entire noise floor up. Do CBs and Ham radio in 10m bands are basically unusable here. @BritishRacingGreen @Coulomb maybe you have some tips? The other inverter of the exact same type generates nothing. What parts would you suggest I check first?
-
Does anyone know why certain inverters work fine with small/cheap AVR generators and others don't?
I saw few mentions that this or that inverter works or doesn't work with cheap AVR generators. All inverters I saw manuals for (Voltronic clones mostly) claim acceptable frequency from 43Hz to at least 63Hz which is a very large range. I see no max THD mentioned anywhere. Does anyone know how to predict a certain AVR generator will work with a certain inverter? Before I even knew about this problem I helped my friends build their tiny system with just 400W solar, single 12V 100ah battery, a 1kW all in one inverter and a 2-stroke petrol generator. They haven't had a problem with the generator until the carb clogged up and started surging. And that is both one of the cheapest inverters and generators I ever saw. Now I've recently bought a new generator, but it will be a while until I can connect it to my system (but I only have 14 days to send it back if I find something I don't like) so I wonder if there is anything I can do to determine this in advance. My generator is a Chinese diesel 9500W (same line of products as this, but with 195FE engine and 7500kW alternator). My inverters are Easun SMH-7k (similar to Voltronic Axpert MKS V) and Y&H 10.2K (also known as PowMR, perhaps Axpert King? I'm not sure).
-
DAXTROMN POWER 2XMPPT 140A 160A ON-GRID/OFF-GRID 10KW 10.2KW -
I'm not seeing the screenshot, but my unit also hasn't got the information about AC input power. Both on lcd and via the rs232. I get load power on AC output, but there is no way to see AC input (in consumption or export). Do you have the right cable? I don't know the pinout of Seplos BMS, but I know the inverter's rs-485 plug uses first two pins of rj45 only. I believe pin 1 is A and pin 2 is B, but I'm not 100% sure it is not swapped. These are the pins that are usually white-orange and orange in typical straight Ethernet LAN cables. There is another standard where these pins are white-green and green. You can tell which you have by looking at what color is at the edge (white-green or white-orange). Comms wise, the inverter runs at 9600 and it has 3 protocols to choose from. I'm using pylontech (with own software battery emulation) but there are two more to choose from. If you can find the BMS pinout and to set it to 9600 bps perhaps it will work with one of the three. Maybe the BMS has a protocol choice too?
-
DAXTROMN POWER 2XMPPT 140A 160A ON-GRID/OFF-GRID 10KW 10.2KW -
Hi, I have two of these, sorry I have no time to read this entire topic now, but let me say both of my inverters are working fine. However, when I got them initially I made a mistake of connecting both PV1 and PV2 in parallel to the same large array and back then it was behaving exactly like you describe. I didn't realise this model has two independent MPPTs and not just a single MPPT with two sets of leads (like some earlier models did). So once I've started using pv1 and pv2 as independent MPPTs it works fine. On the lcd I do get information for one or the other. It cycles depending on up/down press. VIA the rs232 (both the dessmonitor and my own software) there is only voltage for one PV input and total PV charging power available. There is no voltage on another pv input and no "amps per pv input". That is honestly not a big loss, because it is so horrible in measuring current (reporting 7a when there really is 1.5A) that the lack of it is for the better.
-
Inverter lying about power in Watts, but reports correctly in VA.
Ok, I've done more testing... Including with different meters. And I have to say the reality much worse than I expected. For example both of my 10.2kW inverters consistently report over double the current on the PV inputs when it is fairly low. For example. Today (during a very rainy day) I observed the current be around 0.5,0.8A solid. Inverters were consistently reporting 1.6A~1.8A. I never noticed any discrepancy when the current reaches the top limit of the input. Same, but even worse happens on battery input, but here one inverter was a lot better than the other (maybe because one was pulling from the battery and the other was charging?) . The one that was discharging only had about 20% error at ~6A. But the charging inverter was only pushing 1-1.5A into the battery, but it was reporting 7A! This is insane. Since I deployed my system electricity was seemingly "escaping" somewhere. Now I know it has not been escaping. It was being measured very badly. Can someone please comment if this is normal with 10kW voltronic clone inverters? It is as if they are adjusted to measure high range of current at a cost of horribly inaccuracy at low range. Does everyone use external sensors? If so, can someone suggest some hall sensors for the pv? (as precise as possible current up to 30A) Also kwh meters for 240V AC that take into account power factor in their measurements and are easy to get data from? (preferably via local WiFi or serial).
-
Inverter lying about power in Watts, but reports correctly in VA.
I thought I replied after @Coulomb's post, but I must have forgotten to hit submit or something, because I'm not seeing my post... It is second nature to me, but no need to apologise, it is a very valid point 🙂 I always hit a button marked Ref. I also do it right next to where I'll be doing the measurement (before clamping on to the wire) to avoid the possibility of somthing nearby messing with the reading. Interesting and very good to know. I also don't trust my clamp meter that much, but I have 3 inverters hooked up to the same bank of batteries so I can only see combined current on the batteries (on the batteries side I have a Victron Smart Shunt to measure the total and each battery in the bank has its own BMS). I too would prefer self consumption to be included, perhaps the best would be a menu setting, we can wish... Yes, I wonder how precise the SmartShunt really is. It is supposed to have 0.1A precision. At 500A maximum. I have to compare the data with my BMSes, but then which do I trust? It's like in this saying, a man with a watch knows the time, a man with two watches is never sure.
-
Inverter lying about power in Watts, but reports correctly in VA.
You are exactly right. Thank you 🙂 I record the data from my inverters via modbus (a small script I wrote that reports to MQTT, from there it goes to homeassistant and grafana). I got the register numbers here https://github.com/odya/esphome-powmr-hybrid-inverter/blob/main/docs/registers-map.md and they are indeed swapped for VA and Watts. I rarely go to where the inverters are installed in person, but the other night (when there is no load at all on that inverter as only things it powers are washing machine, dishwasher, microwave etc, appliances I know are off when everyone is asleep) and I saw it was reporting about 300VA and almost no Watts of power. So this solves that mystery. Now I have another one... The inverter is supposed to consume 75W idle power (not ideal, but not horrible either). I also measured DC power drawn at the same time(using a DC clamp meter set to 40A) and I saw 2.3A (at 53V). To me this seems pretty excessive. 75W is 1.4A at this voltage. It is set to appliance mode (I heard these inverters consume more in UPS mode, because it has to be always in sync with the grid.). But also I noticed it is in almost perfect sync with the grid when in battery mode even set to appliances. So perhaps this software just pretends to switch to appliance mode? What do you think?
-
Inverter lying about power in Watts, but reports correctly in VA.
Hi, one of my two 10.2kW Y&h inverters (some Voltronic Axpert clone also known under PowMR, Sumry MPS VIII Eco and other brands) is lying about the load power. It is showing 300W load power even in a middle of a night (in battery mode) when nothing is using it. The battery current going in bounces between 0 and 1A so I know it is really only on self consumption of up to ~50W (this is at 53V battery voltage). At the same time Load VA shown much more realistic value that bounces between 18VA to 60VA. I thought perhaps it is some current sensort/transformer, but wouldn't it use the same CT for measuring output current as one used for the VA calculation? My second unit is much better, but still it's load Watts seem 50W too high. Does anyone know if there is some way this can be corrected by setting some internal potentiometer or replacing resistors perhaps?
-
3-phase with 3 standalone(no connections between) all in one inverters?
Yes, they are. I didn't think these details were relevant, but for the sake of completness I'll add more 🙂 I have 14kW peak PV array, but due to max current limitations and the way it is connected it operates at max 9kW peak power (I'm mostly concerned with low light production during rain/winter - I have too much electricity during summer anyway. I currently have 45kWh of battery storage (considering adding 10kWh more as I already have the cells, but they are very bad quality cells so I'm reluctant). This is a single system with 3 hybrid inverters, but not parallell. All inverters are connected to the same battery, but they power different loads. 2 inverters (Y&H 10.2kW) have each half of the array connected to them. The third inverter (EASUN SMH-ii-7k) has no PV currently. All have grid connected (each one has a different phase) and all work in SBU mode. All are configured to charge from the grid only if the battery voltage drops pretty low (which I hope will not happen during the most of the year). There is a transfer switch and a small gas generator (3kW) that can be manually connected to the EASUN inverter to charge the battery if the grid goes down for a long time in winter. I also have a separate purely on-grid single phase system for selling power to the grid. This has a Deye 3kW inverter and 2400W of panels. This system paid for itself in the first 3 years of operation (as I got the panels from a bankrupcy sale and I made the ground mount myself), but the cost of electricity here in Europe is insane now (3x what it was 3 years ago). So the purpose of the current system is to use the grid power as little as possible and where it is inevietable use power "saved" by the on-grid system (although due to recent changes it makes less and less sense to sell power to the grid). The house consumes 10-20kWh per day depending on season and how much we want to save. Everything is electric. The geyser has no tank at all (it is a wall mounted unit that regulates water flow based on set temperature, we set it at 50C) and one can have a normal 10 min shower using only about 1.5kWh of electricity. However when one is not paying attention it is easy to use 5kWh in one use. It is not a lot in the grand scheme of things. But its "the last thing" on the grid in my house so I'm looking into how to switch it too. I'm also considering running the heaters on 240V instead (3 separate phases), but I'm not sure if it will be easy to switch and if it'll work (its a "smart" heater so it may detect the voltage and refuse to run). I'm also thinking about adding an outdoor burried underground tank of hot water, but the cost to do that will be quite high as if I was doing such a big job I'd want the tank to also be used for storing house heating water (I already have a heat pump, but it is currently only used for cooling the house during the summer).
-
3-phase with 3 standalone(no connections between) all in one inverters?
This is not the case. I checked with an oscilloscope. Each inverter synchronises to each own phase from the grid when the grid is on. When grid fails it continues running with this synch, but quickly drifts. So this can be used only for "off grid with grid backup" situations. If it works well one can imagine a tiny 3 phase inverter providing the sync signal for a 100% set up. But its just an idea. There is no comms between inverters (other than my monitoring). They balance loads/PV/battery without any concern what other inverters are doing (to satisfy their each inputs/outputs). Indeed, that's how it looks like. My only reservation is that normally currently flows between live and neutral output. But in a balanced 3 phase set up current flows between phases only. So lets say there is a resistive load (my geyser) and it is delta connected (or star, but fully balanced). Then there will be current on phases, but no current on neutral... But the current has to get back somehow! So what would happen? So this is my only reservation and the reason I haven't tried just connecting it yet. This could be resolved by a relay (to switch off if grid fails) as another user mentioned. Let me add, this is for purely a resistive load. I'd be reluctant to run inductive loads like big motors with this. I have no space in my home for a hot water tank (so I have to run tankless) the geyser is the only load I has to leave on the grid. On the other hand buying a 3 phase system for one load and spending 3x the money is something I decided against.
-
3-phase with 3 standalone(no connections between) all in one inverters?
There are inverters designed to supply 3 phase power. They are connected together and they sync their waveforms by communicating with eachother. This topic is not about tyese. No. I'm talking about the cheap inverters like EASUN SMH-ii (most likely an Axpert MKS II clone with no parallel board). I've done some benchtop testing and I noticed they they sync to the grid exactly even when in SBU mode. So let's say one has a stable 3 phase grid and 3 such inverters that sync to all 3 phases. Can anyone think of a reason why one couldn't use a resistive 3 phase load connected in delta configuration? That resistive load is a tankless water heater (geyser).
-
Meter stopped turning after install
Or enjoy your free electricity from the grid.... Pity it happened now once you have your own system.
-
Borehole pump AC vs DC
Personally I'd invest in a thicker grid cable. For example (if you currently have up to 40V drop with 110m of 7mm2 cable - this is 75A of current): - with 16mm2 copper (around $1100 here in Europe) you'll have 17V drop, perhaps it is acceptable? You would still be loosing almost 10% of power on cable losses. - with 25mm2 copper (about $1700 here) the drop would be much better at 11V - loosing about 850W of power in the cable Do you have access to cheap aluminum ground cables? If I was in your position and I wanted to use the grid I'd probably buy aluminium ground wire 4x50mm2 (this is 50 fifty square mm, not five) like this For the cost of $700 and the voltage drop will be 9V peak. Then you have to bury it of course and you still have the cost of electricity and possibly uncertainty over supply. But it is by far the cheapest outright and easiest option IMO.
-
Why AIO manufacturers warn against grounding battery terminals on AIOs (EASUN, PowMR, SRNE etc) and multiple AIOs on one battery bank.
I was almost certain of it, but when you're repeatedly told otherwise one may doubt. This is an interesting take. Perhaps it was the original intent of the manufacturer. I meant paralleling only the battery connection. Perhaps I should've clarified, but I thought it is obvious as I said in the first sentence of the post: However most people when they talk about "pararelling" mean connecting battery and loads together (or setting up loads as synchronised phases). In this sense you're of course right. Coming back to paralleling-only-the-battery side, unsurprisingly it works fine. I've since connected and tested it in all modes. I plan to resolve the charging issue in the short term by having only one inverter have higher bulk charging voltage than the others. In long term by settings up a "fake bms" connection to all inverters.
-
Why AIO manufacturers warn against grounding battery terminals on AIOs (EASUN, PowMR, SRNE etc) and multiple AIOs on one battery bank.
I'm planning to use multiple AIO inverters powering independent loads with one battery bank (EASUN and Y&H). After researching the topic online including this board I believe this should be fine (providing few small charging issues are met and things like not exceeding max currents). Also after reviewing internal pictures and reading lots of service manuals I noticed all modern AIOs (with HV DC Bus) use a transformer isolated full bridge DC to DC converter for their Battery to HV DC bus connection. So all of them isolate their battery. An example schematic is below: Sometimes there is one transformer. Sometimes there are two (one for the plus leg, one for the minus leg to double the power capacity). But I never saw a non-isolated DC-DC converter for the battery. So if this is the case why are manufacturers warning against grounding the battery? I've recently asked EASUN about grounding the negative terminal of the battery and they replied that "a short will result and damage to the inverter". Are they simply confusing the PV input with the battery? Does anyone know? @Coulomb @BritishRacingGreen no doubt you know the answer to this question. I hope you don't mind me tagging you here 🙂 Edit: This EASUN is a 7.2KV clone of Axpert MKSII, The Y&H I'm planning to use in paralell with it are clones of Axpert MAX 10.2kW.
-
Cheap all-in-one off-grid 10k inverters (Voltronic Axpert Max II etc) can they handle full power?
Just so I understand. So you're considering it good for 5kW, right? Yes, it is half the price of the next "10kW" one, the EASUN SMX. Here in Central/Eastern Europe many of us also don't like to spend too much, buy Deye etc is very popular. At my home I need 24kW of peak load(2*10kw + 7kW inverters) , but my base load is only about ~300W. This high peak is needed when all of the devices are switched on at once which will happen very rarely. So it will have an easy life here. Still it is possible it may ght deliver close to 10kw at some point.
-
Serial port settings for Voltronic/SRNE inverters
I've managed to query data and write certain registers such as battery charging current limit but many registers accept a value, but do not change. I suspect a password has to be sent first. Does anyone know how to do it? What is the register number to send and value? I already tried register number e203 and value of 11111111 in binary. It responds with an error 130 😞 Does anyone know?
-
Serial port settings for Voltronic/SRNE inverters
Hi, I have two inverters, both Voltronic clones (perhaps original design by SRNE). One is an EASUN SMH-ii 7K, the other Y&H 4.2K (same as POWMR 4.2K). For some reason I can;t talk to them via serial RS232 (tried from multiple devices including a USB to rs232 adapter on a windows laptop). I tried 2400 baud (also modbus default in a python library I was using which was 19200) 8N1 settings and no flow control. RTU mode. I suspect these are incorrect settings. Does anyone have the correct ones? I searched online but I couldn't find much. I guess everyone just assumes everyone knows. Short of ripping the cables apart and oscilloscoping the signals I'm not sure how to find this info. I'd rather not destroy the cables so I decided to ask here. Edit: I found the answer - 2400 baud, 8N1 for sure, also a crossover cable.
-
Lower cost hybrid Inverters(Y&h) , how are they different from Off-Grid versions
I wish 😅 Very true(about the difficulty). And this is even without features like parallel operation. I read an article about control mechanisms in parallel inverters to figure out if one could parallel ones without such feature and there are things like circulating currents between two inverters etc to avoid which uses similar control to power factor correction. It's quite a bigger problem than just make sure you supply half the current. Did they publish some info about what cpu/dsp is it? What tool chain they use? What the fw image layout is? Are there some debugging tools onboard? (serial, JTAG etc) Any "entry" points like accessible spi bus for decoded program flash? One would need a spare inverter for sure, just to do some hacking... I actually have all the tools I might need (programmers, interfaces,a fast logic analyser etc). If the 10kW unit from Y&h lives to my expectations I'll be ordering another one to replace my current 4.2kW. So then I'll have the 4.2k as spare to play with. Or are they tight lipped about the actual methods? I'd love to have a go, but reversing it from scratch is such a big task. No surprise someone who invested so much time would want to get dome return on investment. Still I hope for more open information even if it's just the minimum. Now that you say about it I think that's exactly how "tweaking" by manufacturers is done. Unless they do get the source and a nice SDK, but if it existed it would've leaked by now, they are probably doing exact same type of hacking. I've dabbled at such work at various brief times. Mostly as a hobby to crack unknown Cctv cameras to do what I want, but these are simple devices running mostly known type of software (Linux with uboot). Inverters probably running some sort of real time OS might be orders of magnitude more difficult. There is also a possibility they don't have an RTOS and it's written in bare metal code. Depending on the cpu and tools(debugger, emulator) available it may be even better. Id love to find out more. A cool idea. If you ever try please describe the results even if they are negative. I have the same problem. So much stuff to do, so little time!
-
Lower cost hybrid Inverters(Y&h) , how are they different from Off-Grid versions
Very interesting @BritishRacingGreen, thank you for answering. I wish one day someone makes an open source firmware for some of these inverters... I wonder if the source code is floating somewhere (not open source, but known to the people in the know). How else could a bunch of "manufacturers" use the same menus, same features etc?
-
Cheap all-in-one off-grid 10k inverters (Voltronic Axpert Max II etc) can they handle full power?
I'm looking to upgrade my smaller inverters to 10kW and the only unit that looks good price/feature wise is this Voltronic Kodak Max II 10kW clone from Y&h (internal pic shared by another owner attached). Can someone please comment how good or bad they handle close to max AC load? Not momentarily, but let's say for an hour. At 25C or 30C outdoor temp. These radiators don't look that big for 10kW... Here is the inside photo of the clone
-
Lower cost hybrid Inverters(Y&h) , how are they different from Off-Grid versions
But who said anything about "utility approved" 😁 As far as I know none of the Y&h, iGrid, SMX etc are utility approved. But it's not stopping people using them. It is not ideal, I agree completely, but in this thread I wanted to find about about the technical differences in the design between a non-grid export enabled all in one inverter and one with such function. Of course you're right you should not use a non-utility approved device to push to the grid, but people have different needs. For example one may have long running loads and the particular Y&h inverter has an option to limit current to certain amount of amps. So as long as the load is slightly higher there is no actual pushing to grid. But the feature is still called grid export, very confusing for many. This is ideal, but as mentioned being able to set max amps is useful too. Not approved for export, but useful. Both export enabled and ones without export if they advertise 10ms switchover and UPS mode are able to sync to the grid. 10ms is half the grid waveform so to achieve under 10ms switchover they have to sync. Perhaps the ones with grid export "sync better"? More precisely? Yes, this is very important. The models from Y&h I speak of do have "is landing protection" built in. Now we talk about it's use rather than the design of the electronics. It is a separate matter, but yes I agree it doesn't work as good as a grid export inverter with a CT or one that communicates with a smart meter (what you called a relay I guess), for example Deye inverters etc. However a Deye inverter costs 4x the price for the same power so for some people this cheaper grid export is useful too. They don't really have to export to the grid if there is a configurable amps limit. They may have a load exceeding it. Indeed. The kinf of "cheap Hybrid" I talk of has one big shortcoming. As they use the same inverter parts that would normally be supplying loads to do grid export it cannot do grid export and draw from the battery at tye same time. What do I mean? Surely we don't want to export excess pv and use the battery at the same time, right? Imagine the following situation. Your battery is full, the sun is shining and you have a 30A compressor running continously to run some industrial process on the AC in side of the inverter and it's infeasible to change the wiring or it's so powerfull the inverter couldn't start it, but grid export makes it 90% cheaper to run. So you use the grid export . Your "cheap hybrid" also has some computers on the load side. Then a cloud comes and blocks the sun. It stops exporting, this is normal, your compressor runs 100% from the grid, but the inverter also powers the AC out loads (the computers in my example) from the grid despite the full battery. Why? Because you have to switch to SUB to enable grid export. This is how they work. So my main question is, is this just a software feature? Can any all in one inverter with 10ms switchover/ups do such type of grid export in principle? (if it had correct software)
-
Lower cost hybrid Inverters(Y&h) , how are they different from Off-Grid versions
Hi from a new member 🙂 I've been using Solar for quite a while and I have some electronics repair experience. I initially wanted to build a pure off-grid system in addition to my small existing on-grid setup. However, one of the off-grid inverters I bought (Y&h 4.8kW 24v) just to power lights, security system and other small loads has grid tie capability. I tested it and it works pretty well for me. So now I wonder, what is the electrical (or design) difference between off-grid all-in-one inverters that cannot do grid export and those that can. Is it just a software feature? Both types have the one AC inverter for the output (during grid tie it's in bypass-line mode). Both can sync to the grid (as both have the 10ms switchover UPS option). So what functional blocks a typical off-grid inverter lacks to do grid export? By a typical off-grid I mean something like EASUN smh-ii 7k (Axpert MKS ii?). Also, Y&h claim to do their own manufacturing. But main boards look very similar to Voltronic products. Does anyone know if they add the grid export by using custom firmware only? As far as I can tell theirs (Y&h) are the only cheap battery inverters that can do grid export and limit the exported current at the same time. They have new options 37 (enable hybrid mode) and 38 (limit grid tie current) so with some clever programming it is possible to achieve zero export without a CT. I looked at EASUN igrid range and although they can do grid export there is no way to limit. Another notable thing is none of the Y&h inverters can be parallel 'Ed. I'm also interested if this can be changed, but perhaps it's for another thread.