Battery charging via bus bar
Demo, in answer that wont give you 96v in parallel, in series yes, the volts will stay the same in parallel
-
Battery charging via bus bar
sorry there was a typo, not 180A but a 160A
-
Battery charging via bus bar
Its a conderenergy 5kw 24v with 50mm core cables from batteries to 350a bus bar then 90mm core cable from bus bar to 250a disconnect fuse box then into the inverter
-
Battery charging via bus bar
Yes they are connected in parallel, so I should be able to run the inverter at maximum of 180A
-
Battery charging via bus bar
I have 4 x 24v 200AH batteries connected to a bus bar, the spec of the batteries are 100A max continuous charge each, will the 100A be diluted by 4 from the inverter or does that not matter as the amperage will stay the same to each battery no matter how many batteries are connected to the bus bar?
-
Busbars and 250a fuse disconnect
Thanks Stefan, all from the same place👍
-
Busbars and 250a fuse disconnect
I am looking for 350a 5 or 6 pole bus bar (x 2) plus a 250a dipole fuse disconnect. Any help would be appreciated
-
Battery Cable Sizing
That is how I see it as well, thanks HennieL
-
Battery Cable Sizing
the length of the cable to inverter is 970mm, so this must be doubled for both negative and positive
-
Battery Cable Sizing
Sorry late with this info The batteries discharge current is 100A The length of the cable to inverter is 970mm, so we can work off 1m each, I have 4 of these batteries in parallel connected to each other by 200mm cables
-
Battery Cable Sizing
I cut some insulation off and the strands are coated, I scraped some and the strands are copper
-
Battery Cable Sizing
I will cut the insulation and expose the strands and send the pictures for clarification, I used the cable on the left of the first photo
- Battery Cable Sizing
-
Battery Cable Sizing
My 24V 200ah batteries came with what I can measure are 5mm core battery cables, I was not happy so used 8mm core battery cables. My question is why do they supply such thin core battery cables, surely it can be a fire hazard, I have attached a photo for size comparison
-
Conderenergy
Has anyone had experience with Conderenergy inverters, specifically the model S-2752, 5kw 24V. I have not heard of this make.