Moe Joe reacted to PowerUser in Sunsynk - CT ClampIf the distance is too long, maybe this solution will work for you:
https://www.sunsynk.org/post/eastron-meters-do-you-need-one
-
Moe Joe reacted to Scorp007 in Sunsynk - CT ClampYes the 1st try is with Cat 5/6 cable.
If no luck then as per the link provided earlier by @PowerUser
Just don't use 2 pairs to get a thicker wire as the 2 pairs will loose the essential twisted affect.
-
Moe Joe reacted to Steve87 in Sunsynk 8kW / Freedom Won 15/12Further news to the whole CT coil extension. We abandoned the Meter control because the meter simply does not communicate back to the Inverter. We are confident that the Sunsynk sends it's RS485 signal but the meter even though selected does not talk back. We had 2 of these examples on site & they both did not work. The other meter that is supported according to Sunsynk is the Enstrom meter.
I will reach out to Sunsynk support to see exactly why this meter does not work . We extended the CT coil wiring & actually cut the coil wiring off to as small as possible & used Shielded CAT5e cable over a distance of 42m & it worked beautifully. This should give all others trying to do this some confidence.
So for the record the Chint DDSU666 meter is a no go at the moment for Sunsynk 8kW inverter.