JannieO got a reaction from Boerseun in Comms error between VMIII and US3000sI found a solution to the problem courtesy of the supplier (solar-shop.co.za) so I thought it might be helpful to others with the same issue.
1. You have to use the cable supplied with the inverter.
2. Dip switches are 1000 on all batteries (assuming single group).
3. Cable is plugged into master battery RS485 port, not CAN.
Works beautifully.
-
JannieO got a reaction from HennieB84 in Comms error between VMIII and US3000sWhat a painful exercise. Hopefully they can sort it out for you.
-
JannieO got a reaction from HennieB84 in Comms error between VMIII and US3000sHennie yes the cable was included with the inverter when I bought it.
-
JannieO got a reaction from HennieB84 in Comms error between VMIII and US3000sI found a solution to the problem courtesy of the supplier (solar-shop.co.za) so I thought it might be helpful to others with the same issue.
1. You have to use the cable supplied with the inverter.
2. Dip switches are 1000 on all batteries (assuming single group).
3. Cable is plugged into master battery RS485 port, not CAN.
Works beautifully.