I've been running two of these in series on a 24V for a week now and I'm very impressed. I have no reason to doubt the 200Ah capacity rating. The construction looks decent and my (also single page) datasheet had the correct 2S voltages of 25.6V / 27,2V and 28.4V (nominal / float and bulk).
I ran a capacity test lasting 19h and these are my results. The total capacity turned out to be 5.35kWh (rated in 2S configuration is: 25.6V nomimal x 200Ah = 5.1kWh). The higher capacity is due to very low C rate of this test.
One thing I did notice is that the battery voltage is greatly impacted by the load power with increases / decreases in the load clearly visible in the graph below. Note, detailed measurements were stopped after 12h, the load was simply kept constant after this until auto shutdown at 22V after 19h.
Total runtime (h)
19
Ave load (kW)
0.232
Ave discharge rate (C)
0.045
Ave inverter power usage (W)
50
Total kW used by load (kWh)
4.4
Total kWh used by inverter (kWh)
0.95
Total kWh produced (kWh)
5.35