Greetings, I'm trying to figure out BSL 6.4kWh battery settings on an Axpert MKS II 5K off-grid system for cycling in the mid-SOC range of 95% to 15% (80% DOD).

The battery datasheet states

  • Voltage at end of Discharge: 47-48V
  • Recommended Charge Voltage: 55V

The BSL 6.4kWh user manual on the Victron Energy site has these settings for the Quattro 48/5000/70 inverter/charger.
VE Configure Inverter Tab

  • DC input low shut-down: 48.00V
  • DC input low restart: 52.00V
  • DC input low pre-alarm: 49.00V
  • SOC low shut-down: 10%

VE Configure Charger Tab

  • Absorption Voltage: 55.00V
  • Float Voltage: 54.80
  • Charge Curve: Fixed
  • Absorption Time: 1 hour

However, from the General LiFePO4 (LFP) Voltage to SOC charts/tables, 54.80V (float) to 48.00V (LVD) is approximately SOC 99.5% to 9.5% (90% DOD). For the mid-SOC range between 95% (3.363Vpc, 53.80V) and 15% (3.150Vpc, 50.40V), I want to try out the following Axpert settings:


26 - Bulk charging voltage - 54.00V
27 - Float charging voltage - 53.80V
29 - Low DC cut-off voltage - 50.40V
32 - Bulk charging time - 60 minutes

BSL Bull battery users, what are your views regarding these voltage settings? Should I instead consider 90% to 10% SOC range i.e. 53.60V (3.350Vpc) float and 48.00V (3.000Vpc) LVD?

12 hours ago, Kilowatt Power said:

I want to try out the following Axpert settings:


26 - Bulk charging voltage - 54.00V
27 - Float charging voltage - 53.80V
29 - Low DC cut-off voltage - 50.40V
32 - Bulk charging time - 60 minutes

Be aware that the Axperts have the nuisance of the back-to-grid voltage being 2.0 V above the low DC cutoff voltage (undocumented).

Your proposed float voltage is very close to the bulk charge voltage, which is not good for battery life. But you may be more interested in load shedding preparedness.

  • Author
12 hours ago, Coulomb said:

Be aware that the Axperts have the nuisance of the back-to-grid voltage being 2.0 V above the low DC cutoff voltage (undocumented).

 

Hi Coulomb, the installation is completely off-grid with solar only charging. Do settings 12 (back to utility) and 13 (back to battery) matter in this case?

  • Author
12 hours ago, Coulomb said:

Your proposed float voltage is very close to the bulk charge voltage, which is not good for battery life

Noted. I'll use the float voltage stated in the Victron manual (54.80) as the absorption voltage then keep float voltage at 53.80

26 - Bulk charging voltage - 54.80V
27 - Float charging voltage - 53.80V
29 - Low DC cut-off voltage - 50.40V
32 - Bulk charging time - 60 minutes

 

On 2022/02/16 at 3:36 AM, Kilowatt Power said:

I'll use the float voltage stated in the Victron manual (54.80) as the absorption voltage then keep float voltage at 53.80

It's the time spent at high cell voltages that reduces life, not the difference between the absorb and float settings. So I would reduce the float voltage, rather than raise the bulk/absorb voltage.

  • Author
11 hours ago, Coulomb said:

It's the time spent at high cell voltages that reduces life, not the difference between the absorb and float settings

Thanks for spelling this out. It's now perfectly clear and understandable.

Edited by Kilowatt Power

  • Author
On 2022/02/15 at 8:30 PM, Kilowatt Power said:

Do settings 12 (back to utility) and 13 (back to battery) really matter in an off-grid situation? The site will not be connected to grid in the foreseeable future. 

 

On 2022/02/16 at 3:30 AM, Kilowatt Power said:

the installation is completely off-grid with solar only charging. Do settings 12 (back to utility) and 13 (back to battery) matter in this case?

Oops, I missed that post. No, those settings are for "back to grid" and "back to battery from grid". Since you have no grid, you will presumably use the "utility first" output source priority, meaning that if and when generator voltage is present, you will want to use it to power the loads and possibly charge the battery.

  • Author
1 hour ago, Coulomb said:

meaning that if and when generator voltage is present, you will want to use it to power the loads and possibly charge the battery

Thanks. There's a 15 kVA DG set at site which has more or less been decommissioned since the 9.6kWp solar array fills up the 3 x BSL 6.4 kWh batteries in about 2 hours. We have more than sufficient sun at the equator 😉 