Overload alarm on Grid supply

Featured Replies

Greetings

I have attached an image and also a short video regarding my query.

My question:

Does the invertor have internal protection when in bypass?

Not sure if that is the correct question, but from the attached please compare my question.

On 2022/05/06 at 8:46 PM, ayjayaych said:

Does the invertor have internal protection when in bypass?

There's a resettable thermal circuit breaker at the bottom of the inverter appropriately rated for your model. This is for output short circuit protection in line/bypass mode.

The manual also recommends installation of a separate AC input circuit breaker between inverter and power source

image.png.2c5438ffafde9ae31707ad81f1089276.png

 

 

  • Author

What I am asking is, why is the overload indicating when the invertor is in line mode. Is the current not bypassing the invertor?

Should this not only function when the invertor is utilised?

All the other protection has been installed. All I am asking is the above with pictures and video.

7 hours ago, ayjayaych said:

Is the current not bypassing the invertor?

The current still flows through printed circuit tracks and two relay contacts. So there is still a limit. 

On a genuine Voltronic, there is a 40A resettable circuit breaker at the AC input. But the Synerji is a clone, so it may not be present. The breaker if present seems to be a quite slow acting one, so as to not nuisance trip on transient loads like motors starting. 

Edit: however, I've just checked the genuine Voltronic firmware, version 73.00, which is the latest for PF0.8 models (which are actually quite old now). I was surprised to learn that they don't actually distinguish between line and battery modes! So 110% of output power for 10.5 seconds will bring up fault code 07, overload, regardless of bypass or battery mode. Maybe the PCB tracks aren't rated for 40 A continuous, as the relay contacts are.

Edited by Coulomb

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.