Kalito Posted September 23, 2017 Posted September 23, 2017 I have a supersilent FAW 22KVA genset alongside my hybrid solar system. We keep it on Off state as it is wired through mains and out put goes via inverter as well. A relay box isolates the two gysers. In other words if utility power goes the Smartgen internal genset ATS activates. The genset will normally run if it is set to Auto (hence its in off or manual mode to prevent it auto starting). When it is run ofcourse the Inverter sees Utility power and treats it as it would real utility power that is disabled if there is enough solar (inverter set to solar priority). Has anyone know whether one can wire these gensets to the inverter in such a way that they "see" utility absence only when the SOC reaches set levels? For instance if say the inverter batt voltage drops to say 48V the inverter ATS is activated and the inverter starts. When SOC reaches "float" (54V) the genset is made to "see" AC back on and hence shuts down? I read in the Axpert manual of a dry contact thingy. which has several states to control such a thing? Currently there is a cable which runs from the house mains to the genset and a control cable then back to the house. Quote
Chris Hobson Posted September 23, 2017 Posted September 23, 2017 15 minutes ago, Kalito said: Has anyone know whether one can wire these gensets to the inverter in such a way that they "see" utility absence only when the SOC reaches set levels? For instance if say the inverter batt voltage drops to say 48V the inverter ATS is activated and the inverter starts. When SOC reaches "float" (54V) the genset is made to "see" AC back on and hence shuts down? Does you genset have an Auxiliary setting? If so then one could start using that. If not then I am afraid it means insert wiring to carry the start/stop signal directly and voiding the warranty. Those gensets are not designed with solar in mind. My own gennie I have on manual as I do not want an hour or two of cloudy weather to trigger the gennie. Kalito 1 Quote
___ Posted September 23, 2017 Posted September 23, 2017 If you have a Victron BMV battery monitor in place, you can use the relay on the BMV to start the genset, if the genset has an remote start option. Kalito 1 Quote
Kalito Posted September 26, 2017 Author Posted September 26, 2017 This is interesting. Thanks. Warranty is not a biggie at this stage. I think it does indeed have an aux facility. BMV is on the cards too. Chris Hobson 1 Quote
Starlight Posted September 4, 2019 Posted September 4, 2019 My generator doesn't equip with ATS (automatic transfer switch). The purpose of the dual power automatic transfer switch is simply to use as common or backup. When the common power suddenly fails or the power is cut off, the dual power switch is automatically put into the standby power supply, (The backup power supply can also be powered by the generator under small load.) to keep the device still running. ATS can detect the mains failure signal. When the mains fails, it can give a control signal to the self-starting end of the generator set in time, so that the unit can start itself and prepare for power supply. If you want to connect your generator to the inverter, you really need to inquire professional engineer since it is electrical equipment. Your genset uses the same controller SmartGen controller with mine. Quote