January 25, 20233 yr Hi all. Just a question on wiring up a Kodak OG 3.24. i am not experiencing any issues, just want to make sure everything is right. I have ran the AC wires from the non-essential loads DB to the inverter with its own dedicated breaker. The earth wire goes from the non-essential loads DB to the battery and the Inverter. From there all three wires from their own feeds go to the essential loads DB. Is this the correct way or should I drive in a new earth spike outside and connect the inverter and battery to this earth spike instead of the non-essential loads DB. TIA
January 25, 20233 yr 56 minutes ago, sjp100 said: Hi all. Just a question on wiring up a Kodak OG 3.24. i am not experiencing any issues, just want to make sure everything is right. I have ran the AC wires from the non-essential loads DB to the inverter with its own dedicated breaker. The earth wire goes from the non-essential loads DB to the battery and the Inverter. From there all three wires from their own feeds go to the essential loads DB. Is this the correct way or should I drive in a new earth spike outside and connect the inverter and battery to this earth spike instead of the non-essential loads DB. TIA Keep a single earth point namely the one connected to the grid. This will be in the non essential DB.
January 26, 20233 yr Always one ONE Earth. If you install earth spikes you connect them to your main earth. Multiple earths only creates issues. Also if an earth spike is installed and no Earth resistivity test is done it doesn't mean anything, just a rod in the ground.