Posted April 13, 20231 yr Hi, I have been reading the forum, I found this post https://powerforum.co.za/topic/17123-pylontech-us3000c-battery-produces-no-output-accepts-no-charge/ where it's explained a problem with the BMS fuse that I guess I have the same issue, but not sure. I was able to build my own cable and connect battery's BMS with BatteryView 3.0.28. I also tried to understand the info provided in history and event logs, however they are totally unreadble for me, I understand almost nothing about the info that are in them. Here are the files Pylontech-BatteryView-Logs.zip, can anyone help me with them, give some advice or share a blog/manual or anything with info about the meaning of the terms that are in the logs? For example, I learnt from here that "SC" means "Short Circuit", etc. Thank you in advance
April 13, 20231 yr To what inverter is it connected ? Are you running comms between battery and inverter ? The battery experienced many high voltage events , i see 55 volts a few times so it likely blew the BMS.
April 13, 20231 yr Tripple post , website is freaking out for some reason . Edited April 13, 20231 yr by Nexuss
April 13, 20231 yr Something happend on the 22-10-06. After that it was being overcharged for about 10 days up to 54-55,2volts before it died. Edited April 13, 20231 yr by Nexuss
April 14, 20231 yr Author Hi @Nexuss, thanks for your reply. This battery was connected to an Axpert King Rack 3KW 48V and by that time I'm sure there was no comunication between battery BMS and inverter. Actually I have two batteries, here are the logs of the other one Pylontech-BatteryView-Logs.zip. This second battery seems to be working, but I'm almost sure that isn't working properly as the after a couple of days working it shuts down. Pylontech-2-BatteryView-Logs.zip
April 14, 20231 yr 22 minutes ago, pepe_santos said: Hi @Nexuss, thanks for your reply. This battery was connected to an Axpert King Rack 3KW 48V and by that time I'm sure there was no comunication between battery BMS and inverter. Actually I have two batteries, here are the logs of the other one Pylontech-BatteryView-Logs.zip. This second battery seems to be working, but I'm almost sure that isn't working properly as the after a couple of days working it shuts down. Pylontech-2-BatteryView-Logs.zip 279.86 kB · 0 downloads If you still have the other one connected disconnect it asap. The second one is is also going to get fried if its not already. You have to figure out your charging voltages before connecting them again. Pylontech wil most definitely not honour a warranty on those batteries as they have seen lots of abuse ,cells of both packs have reached 3,7V so the cells are likely also compromised now.
April 14, 20231 yr looks like there is something wrong with the second battery aswell ,lots of short circuit errors. Edited April 14, 20231 yr by Nexuss
April 14, 20231 yr 44 minutes ago, pepe_santos said: Hi @Nexuss, thanks for your reply. This battery was connected to an Axpert King Rack 3KW 48V and by that time I'm sure there was no comunication between battery BMS and inverter. Actually I have two batteries, here are the logs of the other one Pylontech-BatteryView-Logs.zip. This second battery seems to be working, but I'm almost sure that isn't working properly as the after a couple of days working it shuts down. Pylontech-2-BatteryView-Logs.zip 279.86 kB · 1 download Hi @pepe_santos i am sorry about this loss, I hope you will come good with this problem. Do you have solar on that King inverter.? Also do you have logger on the inverter? Edited April 14, 20231 yr by BritishRacingGreen