April 17, 20233 yr Good day Just a question for the clever ones. I you install 2 5kw Infini V2 5Kw inverters in parallel, does the charging capabilities then double as well? In other words from 80A it goes to 160A?
April 17, 20233 yr 3 hours ago, Lionheart said: I you install 2 5kw Infini V2 5Kw inverters in parallel, does the charging capabilities then double as well? In other words from 80A it goes to 160A? Assuming that they work like the Axperts, and I believe that they do, yes you get twice the charging current. But each inverter still talks about its own 80 A. You can have different limits in the two inverters, e.g. 60 A on one and 50 A on the other, for a total of 110 A. So you still have 10 A "resolution" on the maximum charge current setting, not 20 A.