3kw 24v Plug & Play without DB

Featured Replies

Hi, greetings.

I have an axpert 3kw hybrid inverter with 2 x 200Ah deep cycle LA, with 100A Fuse between battery and inverter.

I have connected the AC input to a wall socket 20A as the inverter has an AC input of 16.9A and output is 13A.

The AC output is connected via cable to a multi-plug.

System will only be running 2 x TV and 2 x dstv modems. 

Is this correct, and may I use the AC input from wall socket on this system ?

I have not plugged anything in yet.

Edited by 00Dumb

  • Author

ONE more question, Earth wires is the picture ok ?

AC input earth, AC output earth, and Inverter earth bound together as one ? Fine ?

IMG_20230510_183527.jpg

IMG_20230510_183520.jpg

  • 00Dumb changed the title to 3kw 24v Plug & Play without DB
1 hour ago, 00Dumb said:

ONE more question, Earth wires is the picture ok ?

AC input earth, AC output earth, and Inverter earth bound together as one ? Fine ?

IMG_20230510_183527.jpg

IMG_20230510_183520.jpg

No problem should be fine earth's are all common.

If you short between Neutral and Earth on the multi plug, does you earth leakage trip? If not, I don't think you have earth leakage protection.

What is the standard on the inverter trolleys, do they have earth leakage protection? 

On 2023/05/12 at 9:52 PM, Vaal said:

What is the standard on the inverter trolleys, do they have earth leakage protection? 

This is the problem with inverter trolleys you suppose to use class 2 (double insulated) appliances only as they do not come standard with earth leakage protection. If you use class 1 appliances ( refrigerators toasters all appliances with an earth connection) you are to wire in an earth leakage on the output side before the multiplug and you need a non permanent bond between earth and neutral on inverter output side.

Edited by TaliaB

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.