Skip to content
View in the app

A better way to browse. Learn more.

Power Forum - Renewable Energy Discussion

A full-screen app on your home screen with push notifications, badges and more.

To install this app on iOS and iPadOS
  1. Tap the Share icon in Safari
  2. Scroll the menu and tap Add to Home Screen.
  3. Tap Add in the top-right corner.
To install this app on Android
  1. Tap the 3-dot menu (⋮) in the top-right corner of the browser.
  2. Tap Add to Home screen or Install app.
  3. Confirm by tapping Install.

Circuit Breaker Size for 550w Solar Panel

Featured Replies

Ola!

I have a Axpert 1kva 12v inverter with a Revov 12v 2.54kwh battery. I've ordered a 550w solar panel to add to the system to reduce the drain on the battery during loadshedding and to help increase the charging current after. I want to have a circuit breaker between the solar pane and the inverter but am unsure around sizing. 

Is a solar fuse better than a DC breaker for this scenario? For a breaker I think a 63a single pole would work but am not sure of whether that amperage is suitable in this case. The inverter's MPPT is 500w max but it's unlikely the 550w panel will ever produce anything over 500w.

Thanks!

5 hours ago, min.emerg said:

Ola!

I have a Axpert 1kva 12v inverter with a Revov 12v 2.54kwh battery. I've ordered a 550w solar panel to add to the system to reduce the drain on the battery during loadshedding and to help increase the charging current after. I want to have a circuit breaker between the solar pane and the inverter but am unsure around sizing. 

Is a solar fuse better than a DC breaker for this scenario? For a breaker I think a 63a single pole would work but am not sure of whether that amperage is suitable in this case. The inverter's MPPT is 500w max but it's unlikely the 550w panel will ever produce anything over 500w.

Thanks!

During cloud edge you might get over 550W but not for more than about 2-5 min. 

Look on you panel they normally quote the maximum fuse size. I rate fuses to operate faster unless it is a slow blow fuse. I would use a fuse the next size higher than the Isc of the panel. Panels do not provide much more current than their Isc. 

Remember the DC SPD as well as the fuse. 

Edited by Scorp007

  • Author
16 hours ago, Scorp007 said:

During cloud edge you might get over 550W but not for more than about 2-5 min. 

Look on you panel they normally quote the maximum fuse size. I rate fuses to operate faster unless it is a slow blow fuse. I would use a fuse the next size higher than the Isc of the panel. Panels do not provide much more current than their Isc. 

Remember the DC SPD as well as the fuse. 

Thanks! The short circuit voltage for the panel is 14A, so will try a 15A fuse. Because the panel's maximum wattage is slightly in excess of the inverter's MPPT, I'd rather the fuse blow that I'll put between the panel and the inverter than the fuse within the inverter.

  • 4 weeks later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.