May 31, 20233 yr Hi folks, I have recently had a solar system installed and have my solar geyser which is controlled by a geyserwise connected on the non essential side. I have set my geyser element to come on at midday and have set the temp to 65 degrees (maximum allowable on geyserwise), however it only heats up to 55 degrees and then the element switches off. Any ideas on why this would be happening ?
June 1, 20233 yr Hi, It appears in some models that you can go to 65 degrees via the element (video on how to change the settings below) If your model only goes to 55 degrees u can use the sun to go higher than that, you would need to heat the water to 55 degrees with the electric element while there is still sun out, and let the sun heat it past that, now during winter and depending on your direct sunlight, u might want to be 55 at around 2pm already via the element, and then let the sun take it to 65 from 2 - 5 pm. You will need to play around with the times for your geyser location specifically
June 1, 20233 yr Does the geyserwise itself switch the element off at 55deg? Or does the geyserwise show as still heating, but it doesn't get hotter, in which case I'd say your mechanical thermostat (at the geyser itself) is set to cutout at 55deg...
June 1, 20233 yr It will show as still 'on' and could be confused with 'still heating' but it will switch off the element according to your settings (55) until the water drops below 55 and will start heating via the element again, much like a normal geyser works
June 1, 20233 yr I imagine the thermostat at the geyser to be set to higher than 55, however if it was 55 then it would be a bit of a co-incidence, but that i guess could also cause it to stop heating at 55 Edited June 1, 20233 yr by TheNinjaCat
June 1, 20233 yr Author 19 minutes ago, markus_m2 said: Does the geyserwise itself switch the element off at 55deg? Or does the geyserwise show as still heating, but it doesn't get hotter, in which case I'd say your mechanical thermostat (at the geyser itself) is set to cutout at 55deg... The 3 flames on the geyserwise turn from solid and start blinking and the geyser temperature just holds temp at 55 degrees. when I look at the current draw on the inverter, it’s gone back to base load so means geyser element is off
June 1, 20233 yr Author 10 minutes ago, TheNinjaCat said: I imagine the thermostat at the geyser to be set to higher than 55, however if it was 55 then it would be a bit of a co-incidence, but that i guess could also cause it to stop heating at 55 The temp setting is set at 65 degrees
June 1, 20233 yr Just now, King_M said: The 3 flames on the geyserwise turn from solid and start blinking and the geyser temperature just holds temp at 55 degrees. when I look at the current draw on the inverter, it’s gone back to base load so means geyser element is off Yeah so the geyser wise is controlling the geyser element and switching it off at 55 degrees. Earlier when i suggested using the sun to heat the water further, it was under the assumption that you had a solar geyser as well, the evacuated tubes for example
June 1, 20233 yr 3 minutes ago, King_M said: The temp setting is set at 65 degrees If the mechanical thermostat is set to 65 then its 100% the geyser wise controller switching the element off at 55, and then you would need to follow the tutorial posted above to set that higher Edited June 1, 20233 yr by TheNinjaCat
June 1, 20233 yr Quote The geyser's thermostat needs to be removed. The geyser temperature probe provided by GeyserWise has a built in probe that measures the temperature in the geyser. It also supplies information to the element whether it should switch on or not https://www.geyserwise.com/wp-content/uploads/2023/05/GeyserWise-Max-installers-manual-2015.07.01.pdf
August 23, 20241 yr Has anyone got a contact for geysewise? The Tasol mail address is not valid? Thanks. Theresa