July 11, 20232 yr Looking for some advice here.... I have 3 Pylontech batteries (UP 5000 x1 + US 3000C x2) which are all at different SOCs. I need them to all be connected to 1 Sunsynk inverter running together in the end. Would it be advisable to connect and fully charge one at time and then connect all 3 together or connect all three together now and let them sort it out themselves UP 5000 = 50% US 3000C = 98% US 3000C = 70% Thanks in advanced
July 11, 20232 yr Not sure if this is the best practice but I would disconnect the two US3000 and charge UP5000 to 70%. Then connect UP5000 and the one US3000 that is on 70% and charge the two to 98%. Then connect all batteries and monitor
July 11, 20232 yr Author 2 hours ago, hoohloc said: Not sure if this is the best practice but I would disconnect the two US3000 and charge UP5000 to 70%. Then connect UP5000 and the one US3000 that is on 70% and charge the two to 98%. Then connect all batteries and monitor Did not think of that option... Thank you