Axpert 4Kw Settings and error.


Thinus
 Share

Recommended Posts

I am new to the blog but have seen many discussions on Axpert settings.

I need advice on my system please.

2 x 4Kw Axpert (One is RCT and the other Mecer) Connected parallel.

18 x 260 w panels connected to both inverters. +_ 4.5kw

8 x Narada 12NDT200 AGM batteries. 200A each. Float charge - 54V . Bulk charge 57.6V.

Settings at this stage:

01    Sbu

02   50A

03   UPS

04   Sds

05   USE

06   LFE

07   LFd

09   50Hz

11   2A     - don't want utility to charge too much.

12   45V

13   50V

16   CSO

23   byE

26   56.4V

27   54.0V

28   PAL

29   45V

30   All

31   Sbe

We are only 2 in the house and the Stove, Washing Machine, Tumble dryer are not connected to inverters. only the geyser which runs on a timer and only comes on mid morning and later in afternoon. (Trying to max the solar time).

Recently my second RCT packed up and I replaced it with the Mecer. Also upgraded both to firmware 72 40 U1.

Everything runs smooth, and then I get a code 80 error. (CAN). I shut everything down, start up and then it lasts for a day or so. 

Can anyone help on setting suggestions and also on the error?

 

Link to comment
Share on other sites

Hi Thinus

The changes I would make is Setting 12 47V or 48V below 48V is a SOC of below 50% your batteries will not last long under those circumstances. Again setting 13 is too low I would set this to 54 or 55V thus you can be sure that you batteries are receiving a decent amount of charge before going back to solar/battery.

Error 80 is a data/communication error check your cabling between the two inverters.

Link to comment
Share on other sites

Thanks for the info. Is there any recommended monitoring system that I can easily install.

Would like to see at a glance the PV input, Load, battery capacity etc. Maybe something with its own screen. I know the Victron stuff don't match.

Link to comment
Share on other sites

1 hour ago, Thinus said:

I know the Victron stuff don't match.

Yup. It shows the values reported by the various devices (ignoring calibration and efficiencies), updated about once a second at most (sometimes even less, CAN bus batteries often send data only every 2 or 3 seconds) so the values on the screen never adds up exactly :-)

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...