Cable Containment

Featured Replies

Hi All

Scenario: LV Panel cabling from panels to combiner box in a roof space. I assume these cables must be in mechanical containment (trunking and or conduit) to avoid damage? As per Sans code 10142 or the appropriate code for solar installations (domestically). Correct? Or is it not required to have containment? Great if someone could give me the relevant SANS section/subsection either way on this.

solar_20231113_082938.jpg

solar_20231113_083653.jpg

solar_20231113_083701.jpg

1 hour ago, Limpopoboy said:

Hi All

Scenario: LV Panel cabling from panels to combiner box in a roof space. I assume these cables must be in mechanical containment (trunking and or conduit) to avoid damage? As per Sans code 10142 or the appropriate code for solar installations (domestically). Correct? Or is it not required to have containment? Great if someone could give me the relevant SANS section/subsection either way on this.

solar_20231113_082938.jpg

solar_20231113_083653.jpg

solar_20231113_083701.jpg

Some installers are heedless when it comes to pv wire installations. All the gp ac wires in the photo is contained in 25mm pvc conduit, why not the single pos and neg dc wires? If it was decided to use 4mm² or 6mm² Surfix or Norsk cable in the roof space it would have been within Sans spesifications but it is single conductors that must be contained in pvc conduit or trunking. If the wire run exceed >50 meters the pv wires needs to be in metal conduit earthed at 1 point. Furthermore the dc pv wires needs to be labeled "DC PV Wires" with intervals if in pvc conduit or Surfix. Care needs to be taken on high voltage pv cables as the dc side of the installation is much less forgiving than the ac wiring. 

1 hour ago, TaliaB said:

Some installers are heedless when it comes to pv wire installations. All the gp ac wires in the photo is contained in 25mm pvc conduit, why not the single pos and neg dc wires? If it was decided to use 4mm² or 6mm² Surfix or Norsk cable in the roof space it would have been within Sans spesifications but it is single conductors that must be contained in pvc conduit or trunking. If the wire run exceed >50 meters the pv wires needs to be in metal conduit earthed at 1 point. Furthermore the dc pv wires needs to be labeled "DC PV Wires" with intervals if in pvc conduit or Surfix. Care needs to be taken on high voltage pv cables as the dc side of the installation is much less forgiving than the ac wiring. 

Thanks for such a great reply around PV wiring. 

I was going to ask about PVC conduit when you showed us the picture of it over the ridge on a roof. I thought it had to be steel? 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.