Designing solar array to match inverter

Featured Replies

Hi,The I'm looking for someone to check my logic when it comes to designing my PV array .

I'm in Cape Town.  I have about 8m by 4.5m space on my north-facing roof for panels (there is a large pool heating mat up there too, taking quite a bit of space, and I'd like to leave room for solar water).

My inverter says:

  • Nominal operating voltage 360v
  • Vmax 500v
  • Isc 18A
  • MPPT range 250-450v

Looks like this was designed for hybrid/grid-tie with around 10-12 panels.

The approach I'm taking:

  • It'll probably be one string.
  • Moderate wattage panels are more cost effective than the high power ones.
  • I need to keep the total Voc below 500V (in fact probably below 450V to leave some wiggle room for a really sunny South African day?)
  • I need to keep the Isc below 18A (not going to be a problem with one string).
  • Within those constraints I presume I might as well design to get as close to the 360v nominal voltage at the "nominal operating conditions (one panel data sheet say: "* Under Nominal Operating Cell Temperature (NOCT), irradiance of 800 W/m2, spectrum AM 1.5, ambient temperature 20°C, wind speed 1 m/s."

I won't be able to generate enough I don't think to carry all my load, but might as well get as close as I can?

Steve

 

 

  • Author
1 hour ago, Javi Martínez said:

I think you are right, but, may be, It would be better a pair of strings, fulling roof completely.

Has your inverter one or two MPPT? Any shadow? 

HI,

No shadow on my roof.  My inverter has one PV input, though I do have two inverters the same.

Elbow

On 2019/01/06 at 3:01 PM, Elbow said:

My inverter says:

  • Nominal operating voltage 360v
  • Vmax 500v
  • Isc 18A
  • MPPT range 250-450v

Looks like this was designed for hybrid/grid-tie with around 10-12 panels

Looking at you figures it looks like your inverter was designed around  strings of 10 72 cell panels and a maximum of 2 strings per MPPT - roughly 6000W per inverter does that make sense? What does the datasheet say?

With your available roof space you looking at a maximum of eighteen  72 cell panels - maybe only sixteen. With two inverters I would go with a single string of 8 or 9 panels per inverter.

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.