Percy J van Rensburg

Featured Replies

Conderenergy 6.5kw inverter trips on 1.1kw borehole pump startup. I have 6 x 450 watt mono panels connected in series, off grid system.  If I change the inverter load properties from SBU to USB will it be possible to use the generator for the strartup rush of about 21amp and then switch the gennerator of for solar to take over the load or will the transfer lapse be to long. Inverter specs say UPS lapse 10m/s Appliances lapse 20m/s .

Thank you

8 minutes ago, percy said:

Conderenergy 6.5kw inverter trips on 1.1kw borehole pump startup. I have 6 x 450 watt mono panels connected in series, off grid system.  If I change the inverter load properties from SBU to USB will it be possible to use the generator for the strartup rush of about 21amp and then switch the gennerator of for solar to take over the load or will the transfer lapse be to long. Inverter specs say UPS lapse 10m/s Appliances lapse 20m/s .

Thank you

It might help to start. Have you checked that the generator can indeed start the pump? 

This is always not a great application of PV. There is always the cloud problem and then the PV might drop below the 1.1kW needed for the pump. 

This is where a battery of high enough current will assist in starting as the panels on their own could never work. 

You don't mention what battery you have connected?

The 10/20 msec you mention is just the transfer from grid to battery power. 

26 minutes ago, percy said:

Yes presently pumping water with 6.5kw generator. connected battery is SVOLT 51.2v  106 ah 5.43 kwh. battery

Have you tried to start the pump say after 11h on a sunshine day. This to ensure battery is recharged after the night before. Also keep it on SBU. 

Then if the inverter trips try it with the generator running under USB as you suggested. 

Have you tested that the generator is actually used as grid on the inverter? If not try it with a light load like fridges to see that it works. These inverters can be fussy about the quality if supply. 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.