More basic queries from new PV system owner

Featured Replies

I have two strings of 5 x 550w JA Solar panels  . My question is this, can I add two more panels to the one string or do the strings have to be equal, meaning six in each ?

Also does the orientation need to be the same ? Both strings face 15 deg N (my prev post I said NW but I subsequently installed compass app on phone) , so could I add the additional two panels mounted against a close by parapet wall which faces 62 deg N (more direct facing to the early morning sun) ? 

Finally what should be used to clean the panels and how often ? I noticed quite of dust caking the surface. 

 

 

 

5 hours ago, ZaOracle said:

I have two strings of 5 x 550w JA Solar panels  . My question is this, can I add two more panels to the one string or do the strings have to be equal, meaning six in each ?

Also does the orientation need to be the same ? Both strings face 15 deg N (my prev post I said NW but I subsequently installed compass app on phone) , so could I add the additional two panels mounted against a close by parapet wall which faces 62 deg N (more direct facing to the early morning sun) ? 

Finally what should be used to clean the panels and how often ? I noticed quite of dust caking the surface. 

 

 

 

It's essential to provide the make and model of inverter. A lot of inverters will be fine with 6 panels per string but one needs to know the maximum input per MPPT and if different directions the 2x MPPTs work much better. 

My one cent:

If you require more power in the morning then place 6 on a bearing of 062 (62Deg N) and the rest 015 (15Deg N).  

I don't think 2 panels alone facing 062 will make a difference.  Will the mppt even start up with only two?

I might be wrong but most people don't recommend mixing azimuth direction per mppt ie on the same mppt having 3 facing N and the other 3 facing NNE. Emphasis being SAME MPPT

 

One string facing N on a mppt and one string facing NNE on the other mppt is recommended.

7 hours ago, ZaOracle said:

I have two strings of 5 x 550w JA Solar panels  . My question is this, can I add two more panels to the one string or do the strings have to be equal, meaning six in each ?

Also does the orientation need to be the same ? Both strings face 15 deg N (my prev post I said NW but I subsequently installed compass app on phone) , so could I add the additional two panels mounted against a close by parapet wall which faces 62 deg N (more direct facing to the early morning sun) ? 

Finally what should be used to clean the panels and how often ? I noticed quite of dust caking the surface. 

 

 

 

Previous post from @AndrewJdc is spot on.

You can have 6 on each MPPT and even if the sizes vary a bit it will be OK as we don't always have the full 1000W/m² of irradiation. 

With 6 you are about 200W per MPPT over the spec of the inverter. I think this won't be a problem. 

9 hours ago, ZaOracle said:

I have two strings of 5 x 550w JA Solar panels  . My question is this, can I add two more panels to the one string or do the strings have to be equal, meaning six in each ?

You have 5 x 550w/ mppt = 2750w/ mppt currently. Now you are asking 7 x 550w= 3850w for mppt1 and 5 x 550w for mppt2. You will be 600w over the spec for mppt1 but that will not be a problem for the Sunsynk 5kw. 2nd question no the 2 strings on different mppts do not have to be equal.

Edited by TaliaB

 

9 hours ago, ZaOracle said:

Also does the orientation need to be the same ?

Golden rule orientation and tilt must be the same on a single input mppt( 1 string/mppt) for best performance. On a 2 string mppt you can have 1 string of equal amount of panels facing east and the same amount facing west into 1 mppt with 2 strings input as they are paralleled entering the mppt this way you don't have peak production at mid-day but you have an equal spread throughout the day.

Edited by TaliaB

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.