Neville Davidson

Featured Replies

Battery charging. .                                                     Hi tks for all the good info I would like some advice. I have 12 vision , 200 ah batteries connected for a 48 v system with two mercer 5 kw invertets for 10 kw what would be a max charge current we are off grid and a good cut of voltage

tks 

Hi Neville

You have 3 strings of 4 battery's , 200Ah per string so a total of 600Ah. For normal Lead Acids we would then recommend charging at 10% of the total bank size, 60 Amp. 

What is interesting though, the spec sheet shows max charging current as 60A (In a single string application), so I guess you can safely go higher than that. 

From what I read here you should be able to go to 180 Amps. I must admit, this is the highest charging current I have seen on a battery and personally I wont go to 180 Amps.   

Vision.JPG.3331040e21a12c5aa4dd7c76c77fb1b2.JPG

14 hours ago, Neville h said:

what would be a max charge current

Just remember that the maximum charge current settings add (they are per inverter). So for example, you could have a maximum charge current setting on one set to 30 A, and the other to 40 A, for a total maximum charge current of 70 A.

A 5 kW Mecer probably has a maximum charge current of 80 A per inverter (depending on the exact model), and the 5 kW of panels could provide about 100 A each (at 50 V battery voltage), more than the inverters can use. So it seems a shame to charge at only 30 A per inverter. Since your batteries seem to be able to take more current than average, and the usual maximum charge rate for lead acid is 0.15 C (15% of the Ah capacity), that would come to 0.15 x 600 = 90 A. So that would be 40 A on one and 50 A on the other, or you could go for 50 on both.

I agree with @Jaco de Jongh that 180 A is probably too much, as three strings of batteries won't share perfectly, so one string would be getting more current than the manufacturer's limit. At a wild guess, I'd say no more than 120 A maximum, but that's just a gut feel.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.