Hi there,

 

I have an inverter that was running with gel batteries and recently installed lithium batteries, about a month back. We recently had a fault in the road that caused loss of power, my inverter kicked in while we were sleeping but died, not sure when. The power came back on and was charging the batteries for at least 4 hours, yet when I did a test but killing the power to the mains, the inverter was beeping as it seemed like the batteries were low. So I don't think they are charging and now I think I must change the settings on the inverter, as its set to default.

 

I have now set the following after doing some research:

 

Bulk: 14.4v - 28.2

Float: 13.6v ( 13.5v for Must 1kva Inverter ) - 27.2

Cut Off: 11.2v - 22.4

 

This is what I have:

 

GeeWiz Axpert 3000VA (3000W) PURE Sine Wave SOLAR Inverter - 50A/1200W PWM (Hybrid)

 

GeeWiz 12100L 1.2kWh 12V 100Ah Lithium Ion LiFePO4 5000 Cycle Battery (FIRST LIFE CELLS) - 3 Year Unlimited Cycles Warranty - 5000 Cycles X 2

 

12.8V  1.2KWh
Rating: 1C
Maximum continuous discharge: 100Amp
Cells: 1st life prismatic LiFePO4
Series: 2, 3 or 4 batteries
Parallel: 4 Batteries
Communication: None
>5000 cycles at 80% DOD
3 Year Unlimited Cycles Warranty

A balancer will be required when using these in series
This battery has been built with cells that are designed for 5000 cycles (and comes with a 3 year warranty)

 

Battery Voltages

Bulk: 14.4v

Float: 13.6v ( 13.5v for Must 1kva Inverter )

Cut Off: 11.2v

Specifications

12.8V  1.2KWh
Rating: 1C
Maximum continuous discharge: 100Amp
Cells: 1st life prismatic LiFePO4
Series: 2, 3 or 4 batteries
Parallel: 4 Batteries
Communication: None
>5000 cycles at 80% DOD
3 Year Unlimited Cycles Warranty


Features

High Cycle Life and Service Life
High Performance Lithium battery
Internal Battery Management System
Excellent high temperature performance
High energy density and conversion efficiency
Can be configured in 12V, 24V, 36V or 48V in series
Easy drop in replacement for old lead acid battery installs
BMS protects internal cells and ensures smooth operation
Compatible with most UPS & Inverters using AGM/VRLA charge setting
Built-in protection for over-charge, over-discharge & over-temperature
External cell balancer required when placing in series to ensure balancing
Perfect replacement Lithium solution for upgrading your lead acid installation

 

Thank you

Edited by Ariel

20 minutes ago, Ariel said:

Hi there,

 

I have an inverter that was running with gel batteries and recently installed lithium batteries, about a month back. We recently had a fault in the road that caused loss of power, my inverter kicked in while we were sleeping but died, not sure when. The power came back on and was charging the batteries for at least 4 hours, yet when I did a test but killing the power to the mains, the inverter was beeping as it seemed like the batteries were low. So I don't think they are charging and now I think I must change the settings on the inverter, as its set to default.

This is what I have:

 

GeeWiz Axpert 3000VA (3000W) PURE Sine Wave SOLAR Inverter - 50A/1200W PWM (Hybrid)

 

GeeWiz 12100L 1.2kWh 12V 100Ah Lithium Ion LiFePO4 5000 Cycle Battery (FIRST LIFE CELLS) - 3 Year Unlimited Cycles Warranty - 5000 Cycles X 2

 

12.8V  1.2KWh
Rating: 1C
Maximum continuous discharge: 100Amp
Cells: 1st life prismatic LiFePO4
Series: 2, 3 or 4 batteries
Parallel: 4 Batteries
Communication: None
>5000 cycles at 80% DOD
3 Year Unlimited Cycles Warranty

A balancer will be required when using these in series
This battery has been built with cells that are designed for 5000 cycles (and comes with a 3 year warranty)


Features

High Cycle Life and Service Life
High Performance Lithium battery
Internal Battery Management System
Excellent high temperature performance
High energy density and conversion efficiency
Can be configured in 12V, 24V, 36V or 48V in series
Easy drop in replacement for old lead acid battery installs
BMS protects internal cells and ensures smooth operation
Compatible with most UPS & Inverters using AGM/VRLA charge setting
Built-in protection for over-charge, over-discharge & over-temperature
External cell balancer required when placing in series to ensure balancing
Perfect replacement Lithium solution for upgrading your lead acid installation

 

Thank you

 

We need more information to assist with your problem. Did you fully charge each lfp battery, before connecting them in series? Do you have solar panels connected to the Pwm of the inverter? What is the program settings on the inverter. Supply us settings on program 01,02,05,11,12,13,16,26,27,29

  • Author
3 minutes ago, TaliaB said:

We need more information to assist with your problem. Did you fully charge each lfp battery, before connecting them in series? Do you have solar panels connected to the Pwm of the inverter? What is the program settings on the inverter. Supply us settings on program 01,02,05,11,12,13,16,26,27,29

Hi, I don't have solar, no I did not fully charge the batteries, they were just installed  on 20th of June but the power has not gone off since they were installed.

The settings were not changed before, I just changed the following settings now to match the info I was given with the batteries:

 

Bulk: 14.4v - 28.2

Float: 13.6v ( 13.5v for Must 1kva Inverter ) - 27.2

Cut Off: 11.2v - 22.4

Edited by Ariel

5 minutes ago, Ariel said:

Hi, I don't have solar, no I did not fully charge the batteries, they were just installed  on 20th of June but the power has not gone off since they were installed.

The settings were not changed before, I just changed the following settings now to match the info I was given with the batteries:

 

Bulk: 14.4v - 28.2

Float: 13.6v ( 13.5v for Must 1kva Inverter ) - 27.2

Cut Off: 11.2v - 22.4

Is program 05 set to USE as default would be AGM? What is program 02 and program 11 set at? Bulk is fine at 28.2v and float is ok at 27.2v but i will change Cut Off to 25.6v at 22.4v the batteries are less than 10%Soc.

  • Author
9 minutes ago, TaliaB said:

Is program 05 set to USE as default would be AGM? What is program 02 and program 11 set at? Bulk is fine at 28.2v and float is ok at 27.2v but i will change Cut Off to 25.6v at 22.4v the batteries are less than 10%Soc.

I changed program 05 to USE when I changed the settings above.

Program 02 is SOA

Program 11 is 30A

The highest I could set cut off to is 24, is this ok?

13 minutes ago, Ariel said:

I changed program 05 to USE when I changed the settings above.

Program 02 is SOA

Program 11 is 30A

The highest I could set cut off to is 24, is this ok?

Yes 24v is fine 3v/ cell. Do you have a multimeter? If you do have check the voltage of each battery and record the voltage. You will have to put a battery balancer between the 2 batteries to keep them relatively at the same soc. Below link for the balancer.

https://www.geewiz.co.za/battery-balancers/185924-lithium-24v-battery-balancer-equaliser-suitable-for-all-battery-types-24v-2x-12v-batteries.html

  • Author

Hi, thanks so much for your help!

Yes I already have that installed.

I have this Konnwei BK100 Wireless BT Car battery tester 100-2000 CCA 6V 12V - https://www.autosupply.co.za/product/konnwei-bk100-wireless-bt-car-battery-tester-100-2000-cca-6v-12v-bte-bk100/ - Though this I used to test my gel batteries, not sure if I can test Lithium with it.

I think I must let it charge for longer before I test it, I did earlier after only 4 hours of charging but it said something was odd about the voltage.


 

WhatsApp Image 2024-07-13 at 19.23.00_89ef41a8.jpg

Edited by Ariel

  • Author

Assuming the battery tester I have works for Lithium batteries, does this look right? Is my one battery just needing a good charge that the score is so low?

IMG-20240713-WA0013.jpg

IMG-20240713-WA0014.jpg

IMG-20240713-WA0015.jpg

IMG-20240713-WA0016.jpg

9 hours ago, Ariel said:

Assuming the battery tester I have works for Lithium batteries, does this look right? Is my one battery just needing a good charge that the score is so low?

IMG-20240713-WA0013.jpg

IMG-20240713-WA0014.jpg

IMG-20240713-WA0015.jpg

IMG-20240713-WA0016.jpg

Switch the inverter off remove the link in your picture below and test each battery individually i assumed that you did above tests with the series link intact. I don't know the tester you are using but give it a try without the link.

Ps after reading the specs of your tester i don't think the tester is compatible with Lfp or any lithuim battery.

Compatibility – It is compatible with all 6 volt and 12 volt lead-acid batteries, including regular flooded, AGM flat plate, AGM spiral, GEL, and EFB batteries with testing range of 100-2000 CCA. Compatible with cars, motorcycles, trucks, RVs, ATVs, SUVs, boats, yachts, mowers, and even golf carts

WhatsAppImage2024-07-13at19_23.00_89ef41a8.thumb.jpg.50e5b3b343a53c50f49fd14cdfea09ff.jpg.4d6cc252ebaa72a39f7fa76a67f43184.jpg

 

Edited by TaliaB
Added comments

11 hours ago, Ariel said:



I think I must let it charge for longer before I test it, I did earlier after only 4 hours of charging but it said something was odd about the voltage.
 

Yes something is odd here if I may but in. 

If the 2 batteries were charging for 4hrs there should be enough power in them to switch the inverter on and run a low load like laptop or TV at least for enough time. Even if the 2 batteries are out of balance. 

If the above can work just measure the voltage of each battery at the start of this basic test and provide the readings. 

Also check what current the inverter reports during charging if available on the screen. 

As your pictures show the 2 batteries at different SOC I would disconnect both. Use another piece of wire as per your series connection. 

Connect the 2xpos together and the 2xneg to put both in parallel and leave for about 3hrs. Do this with balanced disconnected. They would then balance faster than using the balancer. The balancer works gr8 ongoing. 

Just my 2c.

Edited by Scorp007

  • Author
On 2024/07/14 at 8:15 AM, TaliaB said:

Switch the inverter off remove the link in your picture below and test each battery individually i assumed that you did above tests with the series link intact. I don't know the tester you are using but give it a try without the link.

Ps after reading the specs of your tester i don't think the tester is compatible with Lfp or any lithuim battery.

Compatibility – It is compatible with all 6 volt and 12 volt lead-acid batteries, including regular flooded, AGM flat plate, AGM spiral, GEL, and EFB batteries with testing range of 100-2000 CCA. Compatible with cars, motorcycles, trucks, RVs, ATVs, SUVs, boats, yachts, mowers, and even golf carts

WhatsAppImage2024-07-13at19_23.00_89ef41a8.thumb.jpg.50e5b3b343a53c50f49fd14cdfea09ff.jpg.4d6cc252ebaa72a39f7fa76a67f43184.jpg

 

Hi, you are right I don't think its compatible, I have someone coming to install something on DB board and he will test the voltage for me.

  • Author

Hi, 

So I had the voltage checked: 13.1 and 13.2.

I then did a test with a gaming computer and 65 inch tv on:

Computer and TV on
234 input and output 
Power turned off at 10:36
Input 228
Battery displays 3/4 cells
 
12:36 - 2 hours later
Battery displays 3/4 cells

13:10
If I turn a light on, it drops to 2 bars with bar 3 flashing. Light turned off straight away, went back to 3/4 cells.

13:36 - 3 hours later 
2 cells remaining 
Power turned back on

3 hours of loadshedding tested.

  • Author

Hi,

I had another question,

There was no loadshedding or anything, we had power coming in from Eskom.

With two computers on, a heater, a food warmer, everything was fine. But then the aircon was turned on without my knowledge and straight away it tripped the inverter. I had to to turn the inverter off and then on again.

I understand that the overall wattage usage is too high and it caused it.

I flipped the changeover switch to Eskom and then turned the inverter off and on.

Is this normal that the inverter struggles with a high load even when there is power coming in from Eskom?

16 minutes ago, Ariel said:

Is this normal that the inverter struggles with a high load even when there is power coming in from Eskom?

Yes especially the startup of the aircon the surge with other loads as mentioned would cause it to trip even with utility connected. Surge Capacity is 2* rated power for 5 seconds.

1 hour ago, Ariel said:

Hi,

I had another question,

There was no loadshedding or anything, we had power coming in from Eskom.

With two computers on, a heater, a food warmer, everything was fine. But then the aircon was turned on without my knowledge and straight away it tripped the inverter. I had to to turn the inverter off and then on again.

I understand that the overall wattage usage is too high and it caused it.

I flipped the changeover switch to Eskom and then turned the inverter off and on.

Is this normal that the inverter struggles with a high load even when there is power coming in from Eskom?

Even having just the aircon starting can/should overload the inverter. 

A 3kW can normally only supply 3kW even if it is connected to the grid. 

For sure the batteries will also battle at the 13.1-13.2V level starting the aircon. 

The bars on the battery level is designed for lead acid and of very little help using lithium. 

  • Author
1 hour ago, TaliaB said:

Yes especially the startup of the aircon the surge with other loads as mentioned would cause it to trip even with utility connected. Surge Capacity is 2* rated power for 5 seconds.

If I flipped the changeover switch to eskom before turning on the aircon, then this would mean that it is bypassing the inverter and it would not cause an overload?

  • Author
40 minutes ago, Scorp007 said:

Even having just the aircon starting can/should overload the inverter. 

A 3kW can normally only supply 3kW even if it is connected to the grid. 

For sure the batteries will also battle at the 13.1-13.2V level starting the aircon. 

The bars on the battery level is designed for lead acid and of very little help using lithium. 

Thank you, so yes must just make sure that my dad, he was the one who did it, does not have so many heating elements on. 

1 hour ago, Scorp007 said:

Even having just the aircon starting can/should overload the inverter. 

Hi @Scorp007i run my Hisense 12000Btu aircon on my Rct vm3 24v inverter the power the aircon uses is 1680watts. I can use the cottage lights plus 2 tv sets and the fridge with the aircon and never had a trip. But then again i have 10kwh battery capacity. But that should not matter if you are utility connected and in pass through.

Edited by Derek3

39 minutes ago, Derek3 said:

Hi @Scorp007i run my Hisense 12000Btu aircon on my Rct vm3 24v inverter the power the aircon uses is 1680watts. I can use the cottage lights plus 2 tv sets and the fridge with the aircon and never had a trip. But then again i have 10kwh battery capacity. But that should not matter if you are utility connected and in pass through.

But don't you have an inverter aircon and not the older type that have a high surge current? 

My Axpert 3kVA would trip out if it exceeds this value when on bypass or from battery. I have never tried the max on battery power only. 

Edited by Scorp007

16 minutes ago, Scorp007 said:

But don't you have an inverter aircon and not the older type that have a high surge current? 

My Axpert 3kVA would trip out if it exceeds this value when on bypass or from battery. I have never tried the max on battery power only. 

No my aircon is not the inverter type the normal wall split unit and i have run it for months now. Ps.I just can't switch the kettle on while the aircon is running otherwise it trips.

Edited by Derek3

9 hours ago, Derek3 said:

No my aircon is not the inverter type the normal wall split unit and i have run it for months now.

That's a big bonus. I just thought it would be like some fridges. I have measured a peak of 1800W on a medium fridge during starting although the fridge would run at 130W.

Edited by Scorp007

5 hours ago, Derek3 said:

No my aircon is not the inverter type the normal wall split unit and i have run it for months now. Ps.I just can't switch the kettle on while the aircon is running otherwise it trips.

Hi Derek i think somewhere there is wires crossed. If memory serves me right your electrician( Skollie) did that 3kw installation in your cottage around March/April 23 as he stil phoned me to ask should he connect the aircon to the essential or non essential side so i told him to the non essential side. I have tested a 20000Btu with my IAMMETER and the startup current is 19~21amps for 486ms then it drops down to 7.3 amps. If the compressor cycles on and off you get that spike. I think because he used the existing db for both essential and non essential you may think it runs through the inverter. Check with Skollie tomorrow and let us know as i am here with @Scorp007on this one don't think the 3kw inverter could start the aircon. 

Looking forward to a favourable reply from your end😂

 

Edited by TaliaB
Edit changed incorrect startup time

22 hours ago, Scorp007 said:

But don't you have an inverter aircon and not the older type that have a high surge current? 

My Axpert 3kVA would trip out if it exceeds this value when on bypass or from battery. I have never tried the max on battery power only. 

 

21 hours ago, TaliaB said:

Hi Derek i think somewhere there is wires crossed. If memory serves me right your electrician( Skollie) did that 3kw installation in your cottage around March/April 23 as he stil phoned me to ask should he connect the aircon to the essential or non essential side so i told him to the non essential side. I have tested a 20000Btu with my IAMMETER and the startup current is 19~21amps for 486ms then it drops down to 7.3 amps. If the compressor cycles on and off you get that spike. I think because he used the existing db for both essential and non essential you may think it runs through the inverter. Check with Skollie tomorrow and let us know as i am here with @Scorp007on this one don't think the 3kw inverter could start the aircon. 

Looking forward to a favourable reply from your end😂

 

Hi guys @Scorp007  @TaliaB i spoke to Skollie today and yes you where right my deepest apologies 🙏 to both you guys the aircon is indeed connected to the non-essential side and is not powered by the 3kva inverter. So yes @TaliaByou where spot on with your statement that it is wired on the non-essential side powered by Escom.

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.