Hi, am battling with two inverters that cut off with a 58 error code as soon as the batteries are full.

Setup: I have two Ecco 5.5kw inverters running in parallel and two Fivestar 6kw running in parallel and all four are connected to the same battery bank of 12 x 5.1kw SVolt Lithium batteries. (All Axpert)

The two Ecco’s service one area and the two Fivestar’s another.

Each of the four inverters has 9 x 550w panels connected in series.

Float settings on all four inverters were set to 54v. (User defined) However, the two Ecco's will continue charging despite the fact that the float was reached, and then the two Five star inverters which is connected to the same battery bank will cut off and show error 58 as soon as the battery bank reach more or less 56.5v. (Possibly also damaging the batteries)

In summary it appears that the two Fivestar’s cutt off because of high voltage on the battery bank because the two Ecco's keeps on charging beyond float voltage?

I have lowered the float charge settings on all four inverters to 53v without success. The two inverters purely carry on charging above the set voltage.

The battery bank is new and all connections are tight. The inverters are all new.

The cut-off and the 58 error is not caused by high loads or spike but rather high volts on the battery side.

The manual, as with most Axpert’s states that error 58 means “output voltage too low” The output voltage on all four my inverters remain steady at 230v.

Any advice will be highly appreciated.

26 minutes ago, PaulJV said:

Hi, am battling with two inverters that cut off with a 58 error code as soon as the batteries are full.

Setup: I have two Ecco 5.5kw inverters running in parallel and two Fivestar 6kw running in parallel and all four are connected to the same battery bank of 12 x 5.1kw SVolt Lithium batteries. (All Axpert)

The two Ecco’s service one area and the two Fivestar’s another.

Each of the four inverters has 9 x 550w panels connected in series.

Float settings on all four inverters were set to 54v. (User defined) However, the two Ecco's will continue charging despite the fact that the float was reached, and then the two Five star inverters which is connected to the same battery bank will cut off and show error 58 as soon as the battery bank reach more or less 56.5v. (Possibly also damaging the batteries)

In summary it appears that the two Fivestar’s cutt off because of high voltage on the battery bank because the two Ecco's keeps on charging beyond float voltage?

I have lowered the float charge settings on all four inverters to 53v without success. The two inverters purely carry on charging above the set voltage.

The battery bank is new and all connections are tight. The inverters are all new.

The cut-off and the 58 error is not caused by high loads or spike but rather high volts on the battery side.

The manual, as with most Axpert’s states that error 58 means “output voltage too low” The output voltage on all four my inverters remain steady at 230v.

Any advice will be highly appreciated.

What voltage settings does the ECCO inverters have? like float, charge. bulk charging voltage etc?

Just now, Stefan Cornelissen said:

wait equalization 64v ? that correct. that should never be that high

43 minutes ago, PaulJV said:

I have set bulk at 56.4, Float at 54v, equalization 64v as prescribed. Also lowered all, with no difference.

Try 54v on all and make sure you are set to user define in settings

Good evening @PaulJV

I have the following questions

9 hours ago, PaulJV said:

Setup: I have two Ecco 5.5kw inverters running in parallel and two Fivestar 6kw running in parallel and all four are connected to the same battery bank of 12 x 5.1kw SVolt Lithium batteries. (All Axpert)

The two Ecco’s service one area and the two Fivestar’s another.

A] Are the AC outputs of the Ecco inverters and Fivestar inverters separate?

B] Why don't you separate the battery bank half for the Ecco inverters and half for the Fivestar inverters?

C] Does the inverters communicate with the batteries?

  • Author

Hi Thank you for your response, herewith some answers:

A] Are the AC outputs of the Ecco inverters and Fivestar inverters separate? Yes, the Eccos service three rental cottages and the Fivestar's service three cottages. Two separate outputs.

B] Why don't you separate the battery bank half for the Ecco inverters and half for the Fivestar inverters? Should some of the houses use a lot of power and some a little, it balance each other out. If all separate, I will have to increase each battery bank. Some people us power in the evenings and some who works from home, during the day.

C] Does the inverters communicate with the batteries? No, I could not get the communication up and running.

  • Author
17 hours ago, Stefan Cornelissen said:

Try 54v on all and make sure you are set to user define in settings

Thanks for the response Stefan, Have tried it without success.

I would not run 2 different make and model inverters from 1 battery pack .

If the bulk charge is set at 26.5 the ecco will charge till set volts hold a few minutes and then return to Float charge .

So best set the bulk and float charge on the ecco to 54 volts .

Edited by GMAC

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.