AC Distribution Box Wiring

Featured Replies

Good morning, Everyone

I will be connecting 3 x 8000kVA Single Phase Inverters in parallel. The system is totally off grid. What would be the best way to combine the 3 ac outputs into 1 supply to the main DB EL? I bought 16mm2 cable, so wiring size shouldn't be a problem.

16mm^2 is rated at around 60A, thus over 12kW, which is more than you need per inverter, 6mm^2 rated at 40A would probably be better, then run this 6mm^2 from each inverter into your DB into a 40A breaker for each inverter, I'd say, making all the cables the exact same length, then from each of the 3 40A breakers, run again 6mm^2 cable of same lengths to your main input switch which should probably be rated at around 100A or even a bit larger. As for the parallel cabling for the master and 2 slave inverters, someone who actually has done, this should chip in with some details...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.