May 4, 20197 yr Hi please help with Axpert invertor settings with Pylontech batteries I have parallel Axpert 5kw invertors and 2 pylontech batteries. So far all working well, however my system switches back to Eskom when batteries are at 60% SOC. What settings on ICC do I need to change so that the invertor only switches to Eskom at 40% SOC.
May 4, 20197 yr 7 minutes ago, IrshadS said: What settings on ICC do I need to change so that the invertor only switches to Eskom at 40% SOC. You probably need to drop your battery cutoff voltage a half-volt or two, possibly more. Two volts above this the Axpert will switch to grid all on its own.
August 15, 20196 yr Author Hi, before Pi, I used the standard settings found on this forum. However, those settings switch to grid at about 60% SOC of pylontech
August 16, 20196 yr 5 hours ago, IrshadS said: standard settings found on this forum Or you could follow the instructions starting on the fourth page of this PDF, for the PIP-5048MS: http://www.mppsolar.com/manual/Pylontech Lithium/Pylontech inverter setup SOP.pdf