Error 72


Werner

Recommended Posts

Hi, I have 2 x 5KW Axpert inverters. Just bought a new 10.5 KW Revov lithium battery pack. I installed it myself and as soon as the batteries supply the load by themselves the inverters cut out and give me an error 72. The voltage output is not stable, it jumps up and down. When I put one inverter of by the off switch, the voltage is stable at around 230. Please can someone help. 
 

Link to comment
Share on other sites

6 hours ago, Werner said:

as soon as the batteries supply the load by themselves the inverters cut out and give me an error 72

Error 72 is "current sharing fault". Check that the current sharing cables are installed correctly per the paralleling guide, and that the wires have not come loose.

Edit: they may well have been disturbed when the battery was changed.

Edited by Coulomb