Solo Posted March 22, 2020 Posted March 22, 2020 I understand that when [05] is set to Use, that this enables [26] [27] [29] What are the results of using Fld and Agm? Fld seems to force 26,27, and 29 to the default values? Does Agm do the same? When would one ever want to use Fld or Agm? It is very confusing to have setting 5 default to Fld, not realizing that it has an impact on other important settings! Quote
Coulomb Posted March 22, 2020 Posted March 22, 2020 24 minutes ago, Solo said: I understand that when [05] is set to Use, that this enables [26] [27] [29] Yes. 24 minutes ago, Solo said: What are the results of using Fld and Agm? Fld seems to force 26,27, and 29 to the default values? Does Agm do the same? Yes, FLD and AGM preset settings 26, 27, and 29 to different sets of values; lower bulk/absorb voltage for AGM. 24 minutes ago, Solo said: When would one ever want to use Fld or Agm? Just for ease of use. I'd never use them. 24 minutes ago, Solo said: It is very confusing to have setting 5 default to Fld, not realizing that it has an impact on other important settings! Yes, the user interface is far from perfect. Solo 1 Quote