Mecer 5KVA, Pylontech Connection Question?


George Basson
 Share

Recommended Posts

Hi Guys,

          I want to connect a remote panel to my Mecer 5Kva inverter connected to 3 Pylontech 2000B batteries.

         I received the cables and a connection card (to swap) if required. 

         The problem I have is the connection of the communication cable between the Batteries and the Inverter. 

         There is no port to connect the cable for the remote Panel

          Any Suggestions Pleas?

 

Link to comment
Share on other sites

3 hours ago, George Basson said:

The problem I have is the connection of the communication cable between the Batteries and the Inverter.

You didn't say exactly what model inverter you have. Most models can't usefully connect from the inverter-charger directly to a Pylontech battery. If there is, it should be to an RS-485 port, not the RS-232 port. The remote display connects to the RS-232 port of the inverter, so there should be no conflict.

Link to comment
Share on other sites

 

17 hours ago, Coulomb said:

You didn't say exactly what model inverter you have. Most models can't usefully connect from the inverter-charger directly to a Pylontech battery. If there is, it should be to an RS-485 port, not the RS-232 port. The remote display connects to the RS-232 port of the inverter, so there should be no conflict.

Coulomb,

              Thanks for your prompt reply. I appreciate it sincerely.

              I am working away from home. I'll give more info ASAP.  The PICs shows the cable from Batteries connected to inverter. Where can I connect the remote panel?

image.png

20200427_081231.jpg

Link to comment
Share on other sites

1 hour ago, George Basson said:

Where can I connect the remote panel?

Exactly where that white cable is now. I'm pretty sure you get no benefit from the white cable; perhaps remove it and see if anything bad happens. All the Axperts use an RS-485 port to talk to the battery's BMS; that's an RS-232 port (similar, but not the same at all).

If somehow there is a use for it, you can plug an extension of that white cable into the "COM OUT" port of the remote panel. I realise that this is unlikely to be convenient. So hopefully you don't need that cable. From the photos, your inverter appears to be an Axpert MKS or an Axpert MKS II (obviously the Mecer equivalents, SOL-I-AX-5M/5P/5NB), none of which supports connecting directly to the BMS. My guess is that either the installer doesn't understand, or is trying to make the installation appear more impressive than it is.

Link to comment
Share on other sites

21 hours ago, Coulomb said:

You didn't say exactly what model inverter you have. Most models can't usefully connect from the inverter-charger directly to a Pylontech battery. If there is, it should be to an RS-485 port, not the RS-232 port. The remote display connects to the RS-232 port of the inverter, so there should be no conflict.

 Thanks.

                I'll try the options and reply ASAP.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...