May 24, 20206 yr Hi i am new to this forum , but would like to ask a question as to get more information. i had to replace a older 4000 watt Highbrid solar inverter with a newer Expert 5000Watt/5KA inverter the older inverter had automatic Equalizing setting but the new Expert inverter does not support or have this function . the max voltage setting for charging on new inverter is 56,4 Volt /14,1 Volt per batt max will this be ok for Flooded batteries , or is there a other way of getting these batteries Equalized, also i want to know is the Inverter manufacturer's forcing us to go to Gel/ pilot or other newer type batteries. Thank you for your help Chris
May 26, 20206 yr Hi Chris Include a photo of technical data on stiker on side of inverter. @Coulomb should be able to give you a informative answer. Regards
May 27, 20206 yr On 2020/05/25 at 3:19 AM, Chris Olivier said: the max voltage setting for charging on new inverter is 56,4 Volt /14,1 Volt per batt max will this be ok for Flooded batteries , All Axpert models go to at least 58.4 V (14.6 V per nominally 12 V battery module). Whether this is OK or not depends on your battery specifications; they vary enormously. On 2020/05/25 at 3:19 AM, Chris Olivier said: the older inverter had automatic Equalizing setting but the new Expert inverter does not support or have this function . I'm surprised, if it really is a recent model. Settings around 30-36 relate to equalisation on recent models.