October 2, 20205 yr Thank you to the very helpful forum, one more question please, I intend to do some DIY during the week, involving welding, grinding and so forth, normal power tools. I do not like the inverter to continuously switch between solar and grid, parameter 23 is set on enable bypass, what I would like to know, can I soft set parameter 2 to utility first or is it better to set inverter AC DB physically to Grid on? I would prefer parameter 2 but only if it will not affect the inverter negatively. Bypass due to swimming pool pump running as well as ironing at the same time
October 4, 20205 yr Either will work. If you use parameter 01, all that welding and grinding power goes through the relays inside the inverter. They are rated to 40 A, so that should be fine, especially if it's only occasional high power use. If you have ICC or other monitoring software, you can make the change from your PC or Pi.
October 4, 20205 yr Author Thank you for the feedback, I do the settings on the inverter lcd, appreciate!