December 2, 20205 yr Hi can any one point me in the right direction. I have 2 Acpert inverters master and slave .And 4 pylontech 3000 batteries my issue is the pylontechs are showing ( full row of green LEDs ) fully charged and the inverters are saying not fully charged and every morning l get a error 4 low voltage.when batteries are still showing nearly fully charged. I cant seem to get to the bottom of it Thanks in advance Steve
December 3, 20205 yr You possibly have default battery voltage settings, which are not suitable at all for Pylontechs. Try the below settings.
December 3, 20205 yr Author Thank you so much for taking the time to respond.will give them a tray later
December 4, 20205 yr Author Hi sorry just a bit confused as the manual l have has setting no 2 is total charge solar and utility Thanks Steve
December 5, 20205 yr 19 hours ago, Steve said: the manual l have has setting no 2 is total charge solar and utility Yes, it's the maximum charge current allowed, solar and utility combined. You need to set this to a value suitable for your battery, so it never gets too much charge current. The setting is a maximum current in amps. In your case with 4 US3000s, that would be 37 * 4 = 148 A, round down to 140 A, to be split over two inverters, so use 70 A each (or 80 and 60 if one of your inverters has more or better-oriented solar panels than the other).